Hi.
We have several (about 7 UPS Back-UPS 500 BK500) in out server room, which stay in touch with each other. We have very limited space in our server room and space is critical for us. That's why I want to know - is it OK to place UPS in touch with each other? Please provide links to documentation, as words without prove in documentation are only hypothesis.
I see that there are no ventilation holes on left and right side of UPS - there is only on upper side of UPS. That seems that UPS can stay in touch with each other.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:16 AM . Last Modified: 2024-03-21 05:38 AM
You are very much welcome, I am glad that I was able to help.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:16 AM . Last Modified: 2024-03-21 05:39 AM
Hi JonPro
Is it stated somewhere in documentation? Does APC provides information of this kind in documentation?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:16 AM . Last Modified: 2024-03-21 05:39 AM
Hi Taras,
Normally I would place them with 2~3 inches of gap between one another. This would permit air from flowing and cooling the UPS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:16 AM . Last Modified: 2024-03-21 05:38 AM
Hi Taras,
You can find it listed on this APC Knowledgebase - [What is the expected life of my APC UPS battery?|http://nam-en.apc.com/app/answers/detail/a_id/8301/kw/ups%20environment]
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:16 AM . Last Modified: 2024-03-21 05:38 AM
JonPro, very big thank you for that information. Now I have prove for my customer what distance should be between several UPS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:16 AM . Last Modified: 2024-03-21 05:38 AM
You are very much welcome, I am glad that I was able to help.