I'm considering purchasing J10 or an S10. It's not clear to me whether the J10 produces a stepped sine wave approximation at all times or only when it's on battery power, i.e. does it produce a true sine wave when running on AC?
Thanks, Stuart
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:32 PM . Last Modified: 1 month ago
Hi Stuart,
The J10 will only output a stepped approximation sine wave when on battery. When online it will output filtered utility power so you will get a normal sine wave.
Hope this helps.
Message was edited by: PowerMan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:32 PM . Last Modified: 1 month ago
How many steps does the modified sine wave have? Are there specific UPs or inverters that have a multi step sine wave (16-32 steps for the full wave)?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:32 PM . Last Modified: 1 month ago
Hi Stuart,
The J10 will only output a stepped approximation sine wave when on battery. When online it will output filtered utility power so you will get a normal sine wave.
Hope this helps.
Message was edited by: PowerMan