Please reply, I would like to connect my high end PC and 27 inch monitor to this UPS (BR1000G-IN).
My specs are
Intel i5-4670k,
Gigabyte Z87- UD3H Motherboard,
Zotac 760 gtx Amp edition Graphic card,
G Skill Trident X - 8 GB DDR3 RAM,
1 Bluray writer,
1 Samsung 840 SSD 120GB,
1 WD Black 1TB
4 internal 140mm cooling fan,
6 USB devices,
PSU - I would use is 600 watt 80 plus gold rated smps, is that enough?
My requirement is a 5 to 10 backup, so that I can save my work and shutdown my PC.
Will the UPS be overloaded by my PC specs, thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:11 PM . Last Modified: 1 month ago
You'd probably want a bit of a buffer for potential overloads when the system is working a little harder at certain times.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:11 PM . Last Modified: 1 month ago
Have you tried the UPS selector tool? UPS Selector - Select your protection needs
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:11 PM . Last Modified: 1 month ago
thanks Bill, I will consider the 1500 model.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:11 PM . Last Modified: 1 month ago
I used the tool, the options are a bit older . However I assume my PC will give BR1000G a load >85% . Does this much load affect the UPS lifetime and performance , Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:11 PM . Last Modified: 1 month ago
I recommend keeping the load at less than 80% so look at the 1500 instead of the 1000. Running at 85% will not affect the lifetime but as the battery ages its ability to sustain the load for X period of time can change.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:11 PM . Last Modified: 1 month ago
You'd probably want a bit of a buffer for potential overloads when the system is working a little harder at certain times.