APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:26 PM . Last Modified: 1 week ago
Whenever the laser printer starrts to print, the XS 1000 starts an alarm that is loud and annoying. How can this be disabled? Tried holding down alarm button for 2 secs, but that did not work and tried holding down alarm button and screen buttons together and did not work.
Any help is appreciated.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:26 PM . Last Modified: 1 week ago
Hi,
The reason the UPS is alarming is because the printer is overloading it. You should unplug the printer from the UPS. Plug it into a surge protector that is plugged into a wall outlet not the UPS or purchase a second UPS that can handle the wattage the printer pulls and utilize that.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:26 PM . Last Modified: 1 week ago
Hi,
The reason the UPS is alarming is because the printer is overloading it. You should unplug the printer from the UPS. Plug it into a surge protector that is plugged into a wall outlet not the UPS or purchase a second UPS that can handle the wattage the printer pulls and utilize that.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:26 PM . Last Modified: 1 week ago
That makes sense, I just didn't realize that was a possibility or the probability.
Thanks for your time and help, much appreciated.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.