I think I posted this in the wrong section earlier...
Can anyone tell me what the highest VA is that I can get from a 15amp UPS?
Also I've got a APC UPS Model# DLA1500, was just wondering where I could get a replacement battery for this for cheap?
Thanks,
G
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:51 PM . Last Modified: 1 month ago
Here's an article I wrote some time ago on how to assemble bare batteries into one of the most common APC RBC, APC RBC7 compatible pack.
http://www.wikihow.com/Assemble-an-APC-Rbc7-Smart-Ups-Battery
In place of Plastic Weld, I tried Gorilla glue and it too works very good, however you need to lay the batteries on the side and secure the two halves with tapes so they don't slide around while the glue is curing.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:50 PM . Last Modified: 1 month ago
The SUM units have the highest output rating in terms of watts.
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUM1500RMXL2U
The DLA1500 uses an RBC7.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:50 PM . Last Modified: 1 month ago
Other spec pages that I saw for different UPS units had a specification saying they were 15 amps, where can I find out how many amps these ones are (The one you mentioned above and others like it)?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:50 PM . Last Modified: 1 month ago
A UPS is rated (per electrical code) for 80% of its plug type. So, that UPS that was posted by EZ Button, the SUM1500RMXL2U, has a 15 amp plug (the 5-15 indicates 15 amps - 5-20 would be 20 amps) on it so it is rated for 12 amps for the output. (80% of 15 amps)
Thus, a UPS with a 20 amp plug is rated for 16 amps.
Hope that answers your question.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:50 PM . Last Modified: 1 month ago
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:51 PM . Last Modified: 1 month ago
Here's an article I wrote some time ago on how to assemble bare batteries into one of the most common APC RBC, APC RBC7 compatible pack.
http://www.wikihow.com/Assemble-an-APC-Rbc7-Smart-Ups-Battery
In place of Plastic Weld, I tried Gorilla glue and it too works very good, however you need to lay the batteries on the side and secure the two halves with tapes so they don't slide around while the glue is curing.