APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:15 PM . Last Modified: 1 month ago
I have 7 old SYBT2's that need to be properly disposed. Does APC have a disposal or refurbish program?
Message was edited by: HansonSE
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:15 PM . Last Modified: 1 month ago
I have 7 old SYBT2's that need to be properly disposed. Does APC have a disposal or refurbish program?
Message was edited by: HansonSE
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:15 PM . Last Modified: 1 month ago
I have 7 old SYBT2's that need to be properly disposed. Does APC have a disposal or refurbish program?
Message was edited by: HansonSE
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.