Hello,
I have a Back-UPS CS 350. I'm currently working on a project that has limited space and would like to know if i can change the size of the battery that is compatible with above mentioned UPS.
DEFAULT BATTTERY: CSB; GP 1272 F2; 12V; 7.2Ah
BATTERY IN QUESTION: YUASA; NP1.2-12: 12V; 1.2Ah
Any help would be greatly appreciated. Thank you.
OverklocK
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:42 PM . Last Modified: 1 month ago
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:42 PM . Last Modified: 1 month ago
Hello,
While YUASA is a brand that's sometimes used for APC products, the VA/hr. is going to throw off your runtime, and probably not even provide the necessary charge for the UPS. I'm sure if KVar is around these boards he can shed more light since it seems he has to have more of a plethora of knowledge of the use of non-APC batteries in APC systems.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:42 PM . Last Modified: 1 month ago
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:43 PM . Last Modified: 1 month ago
sorry it's been so long since i've logged on but none-the-less, thank you so much for your response KVAr...it's precisely the answer i was looking for...you've saved me from blowing up my dog who loves laying near the apc because of it's warmth, lol...so if that's out of the question, any recomendations you can give me on the smallest APC unit that can still keep a car alarm running, and 120V air pump, a few flourescent 15" tube lights (12V), and a bunch of 5v LED's?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:43 PM . Last Modified: 1 month ago
The size would be a matter of how long you want to "keep running"
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:43 PM . Last Modified: 1 month ago
essentially, it would only need to run about 10min...any more than that would be a bonus-=]
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:43 PM . Last Modified: 1 month ago
new question
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:43 PM . Last Modified: 1 month ago
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.