APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:08 AM . Last Modified: Friday
My Backups ES 500 is flashing red about 2-3 times per second, and is chirping quickly, twice (chirp-chirp) every 3 seconds.
The chirp is not the same beeping sound I hear when it is on battery backup.
Seems this may be a re-charging problem?
The user manual does not mention chirps.
I have 3 leds:
1) The red one - not labeled, is the one flashing, 2-3 times per second .
2) The Power ON (Green) is not lit (it is initally, but after about a minute goes oiut and the chirping and flashing start)
3) Replace Battery (not lit)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:08 AM . Last Modified: Friday
Okay...Glad to hear that you are going to upgrade the unit.
Have a nice day!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:08 AM . Last Modified: Friday
John,
This symptom appears to be an internal fault in the unit. However, let me collect some information from you to verify if this issue can be fixed. Provide me the exact model number of the UPS. You can find it on a white bar code sticker at the bottom of the unit. Please verify the battery wires are attached to the battery terminals firmly. If possible, reconnect the battery to the battery wires. Make sure that the UPS circuit breaker is not tripped.
Is the outlet fine?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:08 AM . Last Modified: Friday
I installed the apcupsd for opensuse 11.0 and the gapcmon.
It appears one of the cells is dead as the voltage is reading at 10.6VDC.
I have had this UPS for just over 3 years.
DATE : Mon Jul 06 10:43:16 EDT 2009
HOSTNAME : linux-uj6h
RELEASE : 3.14.3
VERSION : 3.14.3 (20 January 2008) suse
UPSNAME : linux-uj6h
CABLE : USB Cable
MODEL : Back-UPS ES 500
UPSMODE : Stand Alone
STARTTIME: Mon Jul 06 09:22:40 EDT 2009
STATUS : LOWBATT *(I turned the unit off for now to stop the Chirping)*
LINEV : 123.0 Volts
LOADPCT : 0.0 Percent Load Capacity
BCHARGE : 000.0 Percent
TIMELEFT : 0.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
SENSE : High
LOTRANS : 088.0 Volts
HITRANS : 139.0 Volts
ALARMDEL : Always
BATTV : 10.6 Volts
LASTXFER : No transfers since turnon
NUMXFERS : 1
XONBATT : Mon Jul 06 09:25:39 EDT 2009
TONBATT : 0 seconds
CUMONBATT: 1 seconds
XOFFBATT : Mon Jul 06 09:25:40 EDT 2009
STATFLAG : 0x07000040 Status Flag
MANDATE : 2006-04-05
SERIALNO : NB0615010136
BATTDATE : 2000-00-00
NOMINV : 120 Volts
NOMBATTV : 12.0 Volts
FIRMWARE : 824.B1.D USB FW:B1
APCMODEL : Back-UPS ES 500
END APC : Mon Jul 06 10:44:01 EDT 2009
I am due for a larger UPS anyway, so I am upgrading to the APC BACK-UPS RS 1500VA LCD 120V.
The user manual did not specify these indications as to being a partially dead battery.
But it appears to be so.
Tks anyway.
JC
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:08 AM . Last Modified: Friday
Okay...Glad to hear that you are going to upgrade the unit.
Have a nice day!
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.