APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:21 AM . Last Modified: 4 weeks ago
I have a Back UPS RS 800. The batteries have just been replaced. When we had a brief power hit recently, the UPS lit up an overload light and shut everything down instead of keeping everything up. I have checked the total wattage connected and it is less than what the UPS is supposed to provide. What's going on? If it's going to shut down every time there's a power flux, it's useless.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:21 AM . Last Modified: 4 weeks ago
Interestingly, in the past two days, we in the Midwest we have had huge windstorms. We lost power both days. When I lost power, the UPS kept both computers up correctly. What does this say about the problem, that is overloads on power fluxes but works with power outages?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:21 AM . Last Modified: 4 weeks ago
Interestingly, in the past two days, we in the Midwest we have had huge windstorms. We lost power both days. When I lost power, the UPS kept both computers up correctly. What does this say about the problem, that is overloads on power fluxes but works with power outages?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:22 AM . Last Modified: 4 weeks ago
No, this has happened several times, including times when no power flux is happening. It happened once when I was out of town. It shut down my entire server and I had to have someone go there and physically restart it. That is the exact _opposite_ of what a UPS is supposed to do. Why should it shut off and never come back on? There needs to be a better way to handle that. I need to know why it is getting an overload when the totals are below its rating. I have not added any devices to the UPS since it was set up and I have verified the totals again.
Your response sounds like a lot of technobabble. I don't know what makes power 'distorted'. No lights were flickering and no other devices had any problems. What is 'transfer time'? Transfer between what and what? It shouldn't matter if power supplies tried to draw their full capacity. As I have said several times, the total power draw of all the devices connected is less than the rating for the UPS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:22 AM . Last Modified: 4 weeks ago
Hi, i had the same problem and i solved!
I don't know if all of this steps matters but because i have done this way, i wrote it.
-First disconnect everything from apc and the battery (i left only the usb cable),GooD LucK
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.