APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:42 PM . Last Modified: Tuesday
I recently bought a BX1300LCD (1300VA). I was going to exchange it for the BX1500LCD, but it appears that the battery capacity is the same. If you compare the half-load and full-load, it appears the run-times would be the same, if under the same load.
Is it true that BX1500LCD uses same capacity battery?
BX1300LCD
Typical Backup Time
Half Load 18.4 minutes (390 Watts)
Full Load 6.4 minutes (780 Watts)
BX1500LCD
Typical Backup Time
Half Load 16.0 minutes (432.5 Watts)
Full Load 5.3 minutes (865 Watts)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:42 PM . Last Modified: Tuesday
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:42 PM . Last Modified: Tuesday
As the batteries are still prototypes, I can only comment based on what I knew of the BX 1200 and 1500 prior to the LCD series. Both used the same batteries, so the ~40W difference in capacity based on loads seems accurate for the runtime. Just because it's 200VA, does not mean it is also 200W.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:42 PM . Last Modified: Tuesday
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.