Posted: 2021-06-28 09:15 PM . Last Modified: 3 weeks ago
Hi,
This is a used device, about 1 year old. It was in use for three months and then kept in storage until yesterday when I plugged it and let it be the whole day.
The problem is that it doesn't seem to charge. The panel reads :ONLINE, 0 load and 0 charge. No other flags or icons are shown, and it beeps twice every 2-3 seconds. The charge bar is constantly flickering.
I read the manual but it doesn't seem to have an explanation for this situation. Any ideas?
I'm trying to use it as the UPS for two work stations in a small office.
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:15 PM . Last Modified: 3 weeks ago
Jose,
Do you have a multimeter that you can test the batteries with? It seems that the possible reason for the batteries not taking a charge is either a failed battery charging circuit, or the batteries are completely discharged. If the UPS is already a year old, you should take into account some degradation on the batteries. On top of that, it was in storage for approximately 3 months, which means that since they require a recharge of 1x every 90 days, it's very possible the batteries have become completely exhausted and are no longer capable of taking a charge.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:15 PM . Last Modified: 3 weeks ago
Jose,
Do you have a multimeter that you can test the batteries with? It seems that the possible reason for the batteries not taking a charge is either a failed battery charging circuit, or the batteries are completely discharged. If the UPS is already a year old, you should take into account some degradation on the batteries. On top of that, it was in storage for approximately 3 months, which means that since they require a recharge of 1x every 90 days, it's very possible the batteries have become completely exhausted and are no longer capable of taking a charge.