APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:09 PM . Last Modified: 2024-03-20 03:14 AM
I need help identifying this sound
My APC Back UPS ES 550 is making a horrendous clicking/sparking sound. The power led is flickering green (on). It's drawing 10w of power with nothing connected.
The noise could be coming from the speaker or 12v relay (845HN-2C-B-S). It's hard to distinguish since it's so loud and both components are close to each other. I don't see any damaged capacitors or blown fuses.
What is going on here? See the video for the full effect.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:09 PM . Last Modified: 2024-03-20 03:13 AM
Hi sv3nster, The rapid switching of the relay is likely a symptom of a corrupted EEPROM and not that of a faulty relay. I would recommend replacing the unit and forego any repairs. The unit is over 7yrs old and will likely continue to show symptoms of it's age. Best, Secretsquirrel
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:09 PM . Last Modified: 2024-03-20 03:13 AM
I need help identifying this sound
My APC Back UPS ES 550 is making a horrendous clicking/sparking sound. The power led is flickering green (on). It's drawing 10w of power with nothing connected.
The noise could be coming from the speaker or 12v relay (845HN-2C-B-S). It's hard to distinguish since it's so loud and both components are close to each other. I don't see any damaged capacitors or blown fuses.
What is going on here? See the video for the full effect.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:09 PM . Last Modified: 2024-03-20 03:13 AM
Hi sv3vster, I think the sound we're hearing in the video is that of a relay chattering between contacts. This is obviously not a normal condition. The rate at which it's changing states, would lead me to believe that we have a failure of the unit's intelligence. Can you please provide the exact model and serial number of the unit so I may make a recommendation? Thank you! Secretsquirrel
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:09 PM . Last Modified: 2024-03-20 03:13 AM
Turns out it's a bit more difficult than expected to locate that defunct part. It is a double pole double throw (2NO/2NC) 12V 8A relay. I may have found a suitable drop in replacement. According to the data sheet, some of the pins are only off by a small margin. Please let me know your thoughts:
Part No: HF115F-012-2ZS4
(or older equivalent JQX-115F-012-2ZS4)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:09 PM . Last Modified: 2024-03-20 03:13 AM
Hi sv3nster, The rapid switching of the relay is likely a symptom of a corrupted EEPROM and not that of a faulty relay. I would recommend replacing the unit and forego any repairs. The unit is over 7yrs old and will likely continue to show symptoms of it's age. Best, Secretsquirrel
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.