APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:57 AM . Last Modified: 2024-03-22 02:58 AM
I have a problem with the UPS , the story is like this, I went out for 4 month now when i came back to office there is a problem , when the light goes off the UPS also goes turns off and stay off. may I know what is the problem?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:57 AM . Last Modified: 2024-03-22 02:58 AM
Lalit,
How old Is the UPS? Has the battery ever been replaced in the UPS? What lights are on the front of the UPS when it is plugged into the wall outlet? Had the UPS been supporting the connected load during power failure before?
Do you have other Identical working unit? If so, swap the batteries and check if the unit in works fine after power failure.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:57 AM . Last Modified: 2024-03-22 02:58 AM
Lalit,
How old Is the UPS? Has the battery ever been replaced in the UPS? What lights are on the front of the UPS when it is plugged into the wall outlet? Had the UPS been supporting the connected load during power failure before?
Do you have other Identical working unit? If so, swap the batteries and check if the unit in works fine after power failure.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.