Geo SCADA Knowledge Base
Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.
Link copied. Please paste this link to share this article on your social media post.
Originally published on Geo SCADA Knowledge Base by sbeadle1 | June 10, 2021 12:59 AM
📖 Home Back
ViewX asks the server what port to use when the script engine initializes i.e. when a mimic is opened. Each mimic has its own instance of the script engine. If the port is changed on the server, mimics that are currently open on clients will stop working. If the web server is not running (due to port clash with other web services on the server), client side scripting won't work.
This page shows some errors associated with the issue. Please also follow this link for more details: Diagnosing Scripting Connection Errors
Error message "Unknown Error 0x80072efd"
Error message "404 Not Found"
or
Error message "405 Method not allowed"
or
"Permission Denied" (if another instance of SCX was running on the port instead)
If you have a proxy defined in your IE configuration, ViewX will try to use that to talk to the web server. This may not be what you want and depending on your setup it wont work (usually the Unknown Error message). Add exclusions in IE for the Geo SCADA servers if you need the proxy set up.
Go: Home Back
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.