Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
Outstation PSTN Connection Problems
Geo SCADA Knowledge Base
Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for
Show only
|
Search instead for
Did you mean:
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
📖HomeBack When using modems, it is often possible to setup the software and modem such that all appears to be healthy. The modem channel in ClearSCADA shows as Healthy. The modem will dial when required and establish a connection to the remote device. However, when the SCADA attempts to transmit data across the link, no data is actually sent past the modem. As far as ClearSCADA is concerned, it was successfully sent to the modem and the SCADA simply appears to receive no response from the remote device. In actual fact, the data was probably not sent by the modem at all.
Check the PSTN channel object and ensure that the Connection tab has flow control set to "Hardware RTS/CTS".
Many modems require hardware handshaking, using RTS or DTR lines connected to the modem to control the flow of information. If these lines are not used, then the modem may not work. In other cases, connection will work without any flow control and may actually not work if hardware flow control is enabled.