Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
Maximum Object Depth and FullName Length
Geo SCADA Knowledge Base
Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for
Show only
|
Search instead for
Did you mean:
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
📖HomeBack In ClearSCADA there is a the maximum number of levels that an object can have in its full path hierarchy. This includes the $Root group (since all objects start in the $Root group) and the object itself. The maximum number of levels available in versions up to ClearSCADA 2007 are 12, meaning that an object can have a depth including up to 10 groups in the path. From ClearSCADA 2009, the maximum number of levels is increased this to 15.
When defining object names, the total length of the name of the object, including the full path hierarchy is 253 characters. Each level can consist of up to 63 characters.
Maximum Object Depth Exceeded
This error is typically seen when trying to import an sde into a group at a deeper level than the level from which it was exported. It indicates that the action can not be completed as the maximum object depth would be exceeded.
From ClearSCADA 2009 R1, the following more descriptive error message is produced.
Import could not be completed because:
The database's maximum object depth of 15 levels would be exceeded.