Originally published on Geo SCADA Knowledge Base by sbeadle1 | June 10, 2021 03:10 AM
Microsoft has released update KB2661254 for all operating systems including Windows XP Service Pack 3/Vista/7 (32bit & 64bit) and Windows Server 2003/2008 (32bit & 64bit). This update has a direct impact on ClearSCADA (WebX in particular) as it restricts the minimum certificate length to 1024 bits. WebX users who are currently using 512 bit certificates will suddenly find an abrupt change in performance once this update is installed. The effects of installing KB2661254 on systems that use a 512 bit certificate are as follows:
NOTE: ClearSCADA systems using 1024 bit or greater certificates are not affected by this update
There are several possible solutions to this issue for customers who are using 512 bit certificates:
Certificates larger than 512 bits are only supported on CS 2009 R2.4 and above. If purchasing new certificates to replace old ones please note that intermediate certificates are only supported in CS 2010 R3 and above. Most certificate authorities now sell intermediate by default.
The location of the private key and certificate files are defined the the following registry keys:
HKLM\SOFTWARE\Schneider Electric\ClearSCADA\DB\WebSSLPrivKeyHKLM\SOFTWARE\Schneider Electric\ClearSCADA\DB\WebSSLPubCert
The key length for certificates generated by ClearSCADA is defined by the following registry key (needs to be at least 1024):
HKLM\SOFTWARE\Schneider Electric\ClearSCADA\DB\WebSSLKeySize
Certutil -setreg chain\minRSAPubKeyBitLength 512
See http://blogs.technet.com/b/pki/archive/2012/07/13/blocking-rsa-keys-less-than-1024-bits-part-2.aspx for more details.