Creating a Latched Button to Trigger Commands on Up and Down Button Actions
Geo SCADA Knowledge Base
Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for
Show only
|
Search instead for
Did you mean:
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
📖HomeBack It is not uncommon to see a requirement for a button which is shown as depressed when a point is on, and raised when the point is off. The button object in ClearSCADA can be configured to represent the state of the point. It also allows actions to be configured independently for clicking on the button when it is up or down (referred to as the Button Up action or Button Down action).
Configure the Latched Button
Firstly, ensure that the button style is set to "Latched" in the button properties dialog.
Button Properties.PNG
Open the animations for the button. The animation named "Latched" determines when the button will show as depressed. The expression evaluated as true will show the button as latched (or depressed), and the expression evaluated as false will show the button raised.
Any non-zero value will mark the button as latched.
When configuring the button pick actions, you will now be presented with two separate pick actions to be configured: Button Down and Button Up. These are the commands that will be run as the user clicks on the button. Button Down is the pick action run when the button is currently in the Up position and will be clicked down, and similarly Button Up is the action run when the button is to be raised from the latched position.