Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
Controlling a point in ClearSCADA mobile
Geo SCADA Knowledge Base
Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for
Show only
|
Search instead for
Did you mean:
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
This article describes the steps to take in order to control a point (analog or digital) in the ClearSCADA database.
Solution
Follow these steps to control a point from ClearSCADA mobile:
1) In the ClearSCADA configurator go to Global Settings. Right-click and select 'Update Settings'. Set the 'Controls Allowed' field to 'Yes'.
13.png
2) As per the ClearSCADA mobile help manual (search 'control' in the ClearSCADA Mobile - Adminisration Guide), add the MobileControlsAllowed metadata field and label
2.png
3.png
3) On the 'Identification' tab of the point (analog or digital), check the 'Mobile Controls Allowed' checkbox.
4.png5.png
4) Create a 'Mobile Display' object in ViewX
6.png
5) On the mobile device, go to the 'Displays' area to control each point
7.png
8.png
9.png
10.png
6) Verify the changes on the mimic in ViewX or WebX