Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
Connecting to Autosol OPC Server
Geo SCADA Knowledge Base
Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for
Show only
|
Search instead for
Did you mean:
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
When adding an OPC Server to ClearSCADA to connect to AES, the connection type on the Server tab defaults to "In Process" and should be changed to "Local Server" or "Remote Server" as required.
If this has not been done, the following symptoms may arise:
You get an alarm "failed - co-createinstanceex returns 80040154"
You cannot browse tags in the OPC server - "create browser returns 0x80070057, parameter is incorrect"
Configure Data Invalidation Setting
When adding a new OPC point to a scanner, ClearSCADA unregisters all the tags on that scanner and re-registers the tags again (including the new ones). Depending on how the OPC server responds with data, this can result in alarms being triggered (by 0 values) and trends including 0 values. Autosol will return 0 values with a quality of Not Connected. Unfortunately, ClearSCADA still uses this value to record historic data and alarms.
To get around this issue, there is an option in Autosol that means the problems go away. Select the option "Invalidate data when communication is lost" in the properties as shown in the dialog below.