Comtrol Rocketport Error "No Write in Progress"
Geo SCADA Knowledge Base
Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for
Show only
|
Search instead for
Did you mean:
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
📖HomeBack When using a Comtrol Rocketport serial port card from within ClearSCADA, the ports may fail displaying the "No Write in Progress" error in the alarm list.
ClearSCADA drivers require the "Wait on physical transmission before completing write" to be enabled on the Comtrol drivers to work correctly. If this is not checked the Comtrol driver will send two write completion notification, one when it accepts the write and the second when the transmit actually completes. This confuses the ClearSCADA drivers and the error "No Write in Progress" is displayed.
For these systems it may be worth installing the most up to date drivers from http://support.comtrol.com/download as the drivers available on the web site are often more up to date than those shipped with the product. A PC reboot after making changes to the Comtrol settings is recommended as the setting changes are not always dynamic (even if they do not prompt for a reboot).