Comparison Between Internal Points, Database Variables and Parameters
Geo SCADA Knowledge Base
Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for
Show only
|
Search instead for
Did you mean:
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
📖HomeBack ClearSCADA contains a number of objects which can be used to store a value, the following table documents the differences between them to help decide which object type should be used
Property
Internal Point
Database Variable
Parameter
Comment
Database icon
Dark Grey
Yellow
Light Grey
Which data steam are the values stored within?
Data stream
Data stream
Config stream
The choice of which steam is important should you export/import the object via SDE. SDE files only contain the config stream so on import the internal point and database variable will have no value
Permission required to change value
Control
Control
Configure
Generally operators will have the Control permissions but not Configure, this can be used to control who can change the value
Alarms
Analogue and digital: Yes
String and Time: No
No
No
Historic
Analogue and digital: Yes
String and Time: No
No
No
Value change logging
Standard event logging
Standard event logging
Config Changes table, if enabled
Includes in count for licensing?
Yes
No
No
Included data types
Analogue
digital
string
time
Lots, including (array for some):
Boolean,
byte
colour (RGB)
double
floats
strings
time
variants
Postal address
double
grid reference
object link
parameter table
string