Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
ClearSCADA DNP3 Slave not Sending Unsolicited Messages
Geo SCADA Knowledge Base
Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for
Show only
|
Search instead for
Did you mean:
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
📖HomeBack In some cases when ClearSCADA is configured to behave as a DNP3 slave device, although some triggered events have been set as Unsolicited Messages, no unsolicited messaged are ever sent.
This behavior is expected if the master station does not enable unsolicited messages in the slave device. This is sometimes the case with older master station SCADA systems or simple implementations of the DNP3 driver.
According to the DNP3 Technical Specification, the slave device is only allowed to send unsolicited messages with event data in them after the master station has enabled unsolicited messages for the appropriate data classes. Until the slave has had this message the only unsolicited message the slave will send is an empty unsolicited packet to announce itself to the master after start up.
The "Unsolicited Message Generation" field on the slave configuration within ClearSCADA controls whether or not the ClearSCADA DNP3 slave will send the empty unsolicited announcement packet on start-up and whether it will send unsolicited events to the master after being told it can by the master.
If the master never enables unsolicited reporting for the appropriate classes, the ClearSCADA DNP3 slave will never send unsolicited event data. If it did, this would break the DNP3 rules for slave devices.