ClearSCADA 2007 R1.4 Upgrade Strategy
Geo SCADA Knowledge Base
Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for
Show only
|
Search instead for
Did you mean:
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
ClearSCADA 2007 R1/R1.1/R1.2/R1.3 Standalone Server
Shut the server down.
Upgrade the server to ClearSCADA 2007 R1.4.
Restart the server.
ClearSCADA 2007 R1/R1.1/R1.2/R1.3 Main and Standby Servers
Shut the standby server down.
Upgrade the standby server to ClearSCADA 2007 R1.4.
Restart the standby server.
Wait for the server to fully synchronize with the main server and go into the standby state.
Shut the main server down. The upgraded standby server will take over as the main server.
Upgrade the previously main server to ClearSCADA 2007 R1.4.
Restart the previously main server. The server will synchronize with the new main server and go into the standby state.
To take advantage of the numerous improvements in this version, it is strongly recommended that both the servers and clients be upgraded to ClearSCADA 2009 R1.4. See the Release Notes for more information.
Other Versions
To upgrade from versions older than ClearSCADA 2007 R1, please follow the instructions shown in the Upgrade Strategy for ClearSCADA 2007 R1 (using 2007 R1.4 instead of 2007 R1).