Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
Adding New Line Characters To Strings on Mimics
Geo SCADA Knowledge Base
Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for
Show only
|
Search instead for
Did you mean:
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
📖HomeBack Occasionally it is a requirement that a new line character is put in ClearSCADA where it expecting a string, eg. a STRING variable in logic or the TooltipText animation on a mimic.
Depending on where the string is being written to in ClearSCADA, different formats are used.
Mimic animations use the CHR(10) function to indicate a new line. Create a text object on a mimic, right click and choose Animations. Scroll down to the TooltipText or Text property and enter the following:
On the mimic, new lines will be used where CHR(10) is used above.
You cannot directly enter a new line character in the Tooltip box on a mimic item's Properties page. However, if you add the text to the TooltipText animation and put the mimic into run mode, go back into design mode and view the Tooltip box on the properties page, you will see a thin rectangle in place of where the new lines are to be placed. This can be copied (ctrl-c) and used through that text box to indicate a new line. You will need to remember to delete the animation if you do this, as that will overwrite the new text you enter into the Tooltip text box.