Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • SCADA & Telemetry Solutions
  • :
  • Geo SCADA Expert Forum
  • :
  • Re: Visual Studio ClearSCADA Reference's
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49357members
Join Now
242617posts
Join Now

Visual Studio ClearSCADA Reference's

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Geo SCADA Expert Forum
Solved
DavidSkilbeck
Lieutenant DavidSkilbeck
Lieutenant
‎2020-01-29 07:48 PM
0 Likes
6
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-29 07:48 PM

Visual Studio ClearSCADA Reference's

Hi,

cant import below reference's.

Thanks, David.

 

References.PNG

Solved! Go to Solution.

Labels
  • SCADA
Share
Reply

Accepted Solutions
sbeadle
Sisko sbeadle Sisko
Sisko
‎2020-01-30 07:02 AM
0 Likes
0
1142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-30 07:02 AM

Re: Visual Studio ClearSCADA Reference's

Hi, I expect you're trying to build the Notify driver and it's web server/client daemon for Twilio.

This is sample code on github provided to enable ClearSCADA / Geo SCADA customers to create an alarm redirection link to make voice telephone/cellphone calls using the Twilio cloud service. Link: https://github.com/ClearSCADA/notify

 

It's not a simple application - check out the powerpoint in the repo carefully.

 

The reference to ControlMicrosystems.ClearSCADA.DDK will be found in the c:\Program Files\Schneider Electric\ClearSCADA folder - you'll need this for Notify and DriverNotify projects.

 

The reference to Notify.dll will be found in it's compiled folder after it has been built for the first time - build that project first.

 

The DriverNotify project also needs a reference to ClearScada.Client, again find this in c:\Program Files\Schneider Electric\ClearSCADA

 

Finally, the element you'll need to get this to work is a Twilio account, some registered phone numbers and a configured flow. This is described in the powerpoint. The last item is not fully documented, and you will need to customise this but include some essential elements. I'll push an update to the powerpoint to flesh this out more.

 

If you need further help, please get back on this forum with a new post, and include screen pics and error descriptions if possible.

 

If this answers your query please mark it as the solution. 

Best regards, Steve.

 

See Answer In Context

Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
6 Replies 6
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-01-29 07:55 PM
0 Likes
5
1202
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-29 07:55 PM

Re: Visual Studio ClearSCADA Reference's

Why not?


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
DavidSkilbeck
Lieutenant DavidSkilbeck
Lieutenant
‎2020-01-29 08:41 PM
0 Likes
4
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-29 08:41 PM

Re: Visual Studio ClearSCADA Reference's

I can't find the controlMicrosystems reference.
Can find the other two. However, I get no message that they have not installed or any error or issues.

 

 

 
 

References1.PNG

Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-01-29 08:47 PM
0 Likes
0
1184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-29 08:47 PM

Re: Visual Studio ClearSCADA Reference's

Seriously man... provide some information for us to help you.

 

a. How do you think it's supposed to work?

b. Why do you think it's not working?

c. What steps have you followed to try to solve the problem?

 

Like... have you even checked within YOUR Visual Studio project to see what it's complaining about?

I imagine it's something like "I can't find this reference that you told me you have"...

In which case, what makes you think that you have that reference?

Have you installed ClearSCADA / Geo SCADA Expert on this machine?  If you haven't... then duh!!!  It's not like Microsoft ship ClearSCADA as a part of Windows.

 

If you have installed ClearSCADA, and still have these reference complaints, where is Visual Studio looking for the references?

I imagine it's not looking in the same place as ClearSCADA has installed them.  So you should find the referenced DLL files (and Visual Studio is probably telling you exactly what DLLs it's looking for), and then re-point Visual Studio to find them.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
DavidSkilbeck
Lieutenant DavidSkilbeck
Lieutenant
‎2020-01-30 01:43 AM
0 Likes
2
1167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-30 01:43 AM

Re: Visual Studio ClearSCADA Reference's

The issue seems to be with the Notify.dll (presuming that is its file name).
Cannot find it on C drive when searched for.

Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-01-30 01:57 AM
0 Likes
1
1163
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-30 01:57 AM

Re: Visual Studio ClearSCADA Reference's

Easy fix... Notify.dll is not a Schneider supported item as far as I'm aware.

So you should look for some more information from wherever you sourced it from 🙂

 

And given that your second post in this thread showed Notify as a Project Reference within your user directory... I'd say that you should go and speak to yourself about why you don't have a Notify.dll generated from the Visual Studio project that you apparently have which is likely called 'Notify'


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
sbeadle
Sisko sbeadle Sisko
Sisko
‎2020-01-30 07:02 AM
0 Likes
0
1143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-30 07:02 AM

Re: Visual Studio ClearSCADA Reference's

Hi, I expect you're trying to build the Notify driver and it's web server/client daemon for Twilio.

This is sample code on github provided to enable ClearSCADA / Geo SCADA customers to create an alarm redirection link to make voice telephone/cellphone calls using the Twilio cloud service. Link: https://github.com/ClearSCADA/notify

 

It's not a simple application - check out the powerpoint in the repo carefully.

 

The reference to ControlMicrosystems.ClearSCADA.DDK will be found in the c:\Program Files\Schneider Electric\ClearSCADA folder - you'll need this for Notify and DriverNotify projects.

 

The reference to Notify.dll will be found in it's compiled folder after it has been built for the first time - build that project first.

 

The DriverNotify project also needs a reference to ClearScada.Client, again find this in c:\Program Files\Schneider Electric\ClearSCADA

 

Finally, the element you'll need to get this to work is a Twilio account, some registered phone numbers and a configured flow. This is described in the powerpoint. The last item is not fully documented, and you will need to customise this but include some essential elements. I'll push an update to the powerpoint to flesh this out more.

 

If you need further help, please get back on this forum with a new post, and include screen pics and error descriptions if possible.

 

If this answers your query please mark it as the solution. 

Best regards, Steve.

 

See Answer In Context

Share
Reply
Top Experts
User Count
sbeadle
Sisko sbeadle Sisko
1
geoffpatton
Lieutenant geoffpatton
1
BevanWeiss
Admiral BevanWeiss
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric