Hi,
I'm trying to make a dynamic tooltip text, as I want to make a certain object (for example a pump) tell me it's status when I hover over it.
The problem it I'm still having the text show up as a text not a running expression.
the expression is (".Testing.Reservoir.Running.CurrentStateDesc")
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-26 06:55 AM
Well ... 😄
the solution is to write the expression in Tooltip text option in the animation tab not in the properties tab.
i guess it's quite easy 😄 i don't know why it took me so long to make it