Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • SCADA & Telemetry Solutions
  • :
  • Geo SCADA Expert Forum
  • :
  • Re: Tables and Record Id's
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49474members
Join Now
242778posts
Join Now

Tables and Record Id's

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Geo SCADA Expert Forum
Solved
DavidSkilbeck
Lieutenant DavidSkilbeck
Lieutenant
‎2020-11-30 09:00 PM
0 Likes
9
496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-30 09:00 PM

Tables and Record Id's

Hi,

I am trying to use a table as a queue.

 

Using the automation interface I grab the contents of RecordId 0.

xxxxxId = Xobj.Interface.GetValue(1, RecordId);

Then once the code completes actions, RecordId 0 is deleted.

Xobj.Interface.DeleteRecord(0);

The next time round it causes issues as there is not a RecordId = 0 it seems.

If I add to the table, then the new record takes the number 0 and the code runs again for an iteration.

 

My question is, is there a way of getting the table to re order its recordId's.

If the table could shuffle its record Id's. So recordId 1 became recordId 0 etc.

Or do I have to create a column for Id's and reorder this column via code.

Thanks,

 

Solved! Go to Solution.

Labels
  • SCADA
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply

Accepted Solutions
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-12-01 03:44 AM
0 Likes
8
483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-01 03:44 AM

Re: Tables and Record Id's

Does the queue need to be shared amongst all clients, or is it just for a single client?

For a single client, I'd recommend using something like a Scripting Dictionary, or even just a VBscript array or such.

 

If you need a queue across the whole system, then you could have a look at the CVariableArray objects... they might suit your needs better if you only need a few objects.  NOTE: You will almost always have some kind of issues with concurrency here, since there is really no way (I know of) to perform the atomic operations needed for concurrent queue access within GeoSCADA Expert scripting.

 

I'm unsure how the RecordId calculations occur.  I suspect it's got a bit of a disconnect between the client and the server.

So when you do the DeleteRecord(0).. on the server at that exact moment there is still a RecordId 0, but on the client there is no RecordId 0, however there is a RecordId 1.  Some later time the client will synchronise its modification with the server, and then update its data, and you might end up in the situation where there is a RecordId 0 on both the client and the server again... with all other Records having dropped down by an index.

 

I'd really try to avoid it if at all possible.

What you could do is using a DataTable and another column with something like a DateTime (or just a self managed incrementing value).  I'd personally go for the DateTime column, since it is much easier to handle.

When you add something to the 'queue' then you add it with the current DateTime.

To take something out of the queue you just delete the item that matches the TOP (1) FROM DataTable ORDER BY EntryDate ASC.

And do the INSERT / SELECT / DELETE using SQL.

 

There's still the possibility of things going a bit wrong... since you could have multiple clients actioning a remove at the same time, in which case only one can clearly win.  Likewise multiple clients adding something to the queue at the same time brings up the race condition around entry values if using an incrementing value... hence my recommendation to just use a DateTime.  You're more likely to have a unique DateTime than to be able to ensure global consistency on a shared variable. 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
9 Replies 9
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-12-01 03:44 AM
0 Likes
8
484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-01 03:44 AM

Re: Tables and Record Id's

Does the queue need to be shared amongst all clients, or is it just for a single client?

For a single client, I'd recommend using something like a Scripting Dictionary, or even just a VBscript array or such.

 

If you need a queue across the whole system, then you could have a look at the CVariableArray objects... they might suit your needs better if you only need a few objects.  NOTE: You will almost always have some kind of issues with concurrency here, since there is really no way (I know of) to perform the atomic operations needed for concurrent queue access within GeoSCADA Expert scripting.

 

I'm unsure how the RecordId calculations occur.  I suspect it's got a bit of a disconnect between the client and the server.

So when you do the DeleteRecord(0).. on the server at that exact moment there is still a RecordId 0, but on the client there is no RecordId 0, however there is a RecordId 1.  Some later time the client will synchronise its modification with the server, and then update its data, and you might end up in the situation where there is a RecordId 0 on both the client and the server again... with all other Records having dropped down by an index.

 

I'd really try to avoid it if at all possible.

What you could do is using a DataTable and another column with something like a DateTime (or just a self managed incrementing value).  I'd personally go for the DateTime column, since it is much easier to handle.

When you add something to the 'queue' then you add it with the current DateTime.

To take something out of the queue you just delete the item that matches the TOP (1) FROM DataTable ORDER BY EntryDate ASC.

And do the INSERT / SELECT / DELETE using SQL.

 

There's still the possibility of things going a bit wrong... since you could have multiple clients actioning a remove at the same time, in which case only one can clearly win.  Likewise multiple clients adding something to the queue at the same time brings up the race condition around entry values if using an incrementing value... hence my recommendation to just use a DateTime.  You're more likely to have a unique DateTime than to be able to ensure global consistency on a shared variable. 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
DavidSkilbeck
Lieutenant DavidSkilbeck
Lieutenant
‎2020-12-01 12:42 PM
0 Likes
7
471
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-01 12:42 PM

Re: Tables and Record Id's

Thanks Bevan.

Interesting points

 

I'm unsure how the RecordId calculations occur.  I suspect it's got a bit of a disconnect between the client and the server.

 

DateTime

There's still the possibility of things going a bit wrong... since you could have multiple clients actioning a remove at the same time, in which case only one can clearly win.  Likewise multiple clients adding something to the queue at the same time brings up the race condition around entry values if using an incrementing value... hence my recommendation to just use a DateTime.  You're more likely to have a unique DateTime than to be able to ensure global consistency on a shared variable. 

 

Thanks,

 

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
AdamWoodland
Lt. Commander AdamWoodland Lt. Commander
Lt. Commander
‎2020-12-01 05:52 PM
0 Likes
6
460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-01 05:52 PM

Re: Tables and Record Id's

If you do go down the path of a table, you should probably have a datetime and a unique reference like a GUID per row. Then you can use the datetime as a sort and a GUID as a manipulation.

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
DavidSkilbeck
Lieutenant DavidSkilbeck
Lieutenant
‎2020-12-01 06:30 PM
0 Likes
5
456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-01 06:30 PM

Re: Tables and Record Id's

Hi, have I got the syntax wrong to this


SQLStatement = "DELETE TOP (1) FROM XQueue ORDER BY EntryDate ASC"

 

Or is it because I don't have a unique reference like a GUID per row.

 

Thanks,

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-12-02 12:19 AM
0 Likes
4
441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-02 12:19 AM

Re: Tables and Record Id's

If you look at the quite complicated SQL help you'll see that unfortunately your syntax is invalid.

 

You'd need to have something like 

DELETE FROM MyDataTable

WHERE MyGuidGolum =

(

  SELECT TOP(1) MyGuidGolum

  FROM MyDataTable

  ORDER BY EntryDate ASC

)

 

Since you would have already needed to 'peek' the data, you probably should already have a 'cache' of the GUID to reference in the DELETE


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-12-02 11:28 AM
0 Likes
3
428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-02 11:28 AM

Re: Tables and Record Id's

I should probably clarify what I mean in regards to my comment:

I'm unsure how the RecordId calculations occur.  I suspect it's got a bit of a disconnect between the client and the server.

 

I don't mean that the client 'calculates' Record ID separately from the server.  But where a record is removed from the record set, I don't think the client will recalculate new record ids at all.  In which case, the client knows that it has removed the record id in question (say record id 0), but it won't shuffle down all of the other record ids.. since that would likely make it inconsistent with the (authoritative) server version of the table.

When the server gets the update for the record deletion, it would then process that, and send out the updated version to clients after the update.  At that time the client will update its record, and then it might gain a 'new' record id 0 (when the other records 'drop down a slot').

 

This is all hear-say... since I don't know precisely what the code for this looks like in GeoSCADA.. but for a multithreaded environment, it would be quite bad for performance if all client-server interactions had to be synchronised and locking (i.e. if a client thread change to one object prevented all other client access to that object, and all related objects until the server had advised that it had fully processed the change).

More common would be that the client would use an 'offline' or cached version of objects, apply modifications to these, and have a background process to synchronise and update, with locking only performed when absolutely needed for consistency.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
DavidSkilbeck
Lieutenant DavidSkilbeck
Lieutenant
‎2020-12-02 04:53 PM
0 Likes
2
420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-02 04:53 PM

Re: Tables and Record Id's

Hi,

I have tried the below. With no success.

 

'SQLStatement = "DELETE FROM XQueue WHERE EntryDate = (SELECT TOP(1) EntryDate FROM XQueue ORDER BY EntryDate ASC)"

Didn't do anything, just passed through.

 

Then I tried


SQLStatement = "SELECT Top(1) EntryDate FROM XQueue ORDER BY EntryDate ASC"
Set GuideColumn = Server.Query(SQLStatement)


*SQLStatement = "DELETE FROM XQueue WHERE EntryDate =" &GuideColumn &""
Set DeleteRowTable = Server.Query(SQLStatement)

 

* Object does not support this property or method. I have got the end of the statement wrong &"".

But don't know if it would work anyhow?

Thanks,

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-12-03 12:09 AM
0 Likes
1
409
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-03 12:09 AM

Re: Tables and Record Id's

If you're using the GUID as the DELETE filter then it will need to be wrapped based on the datatype.

i.e this is invalid DELETE FROM Table WHERE TextItem = cats and dogs

this is also invalid DELETE FROM Table WHERE DateTimeItem = January 20th 2019

 

The error that you got suggests that you've got a typo or something on the "Server.Query" part.

Since if it were strictly a query issue then I would expect a different error on assignment, or on analysis of the assignment.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
DavidSkilbeck
Lieutenant DavidSkilbeck
Lieutenant
‎2020-12-03 05:48 PM
0 Likes
0
362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-03 05:48 PM

Re: Tables and Record Id's

Hi,

SQLStatement = "SELECT Top(1) EntryDate FROM XQueue ORDER BY EntryDate ASC"
Set GuideColumn = Server.Query(SQLStatement)
GuideColumnRows = GuideColumn.Rows
LatestDate = GuideColumnRows(0,0)
LatestDateLocal = (CStr(UTCToLocalTime(LatestDate)))
AMPM = Right(LatestDateLocal, 2)
If AMPM = "PM" Then
DateLeft = Left(LatestDateLocal, 17)
End If
LatestDateLocal = DateLeft + ".000 " + "PM"
SQLStatement = "DELETE FROM xQueue WHERE EntryDate ='"&LatestDateLocal&"'"
Set DeleteRowTable = Server.Query(SQLStatement)


Gave up in the end. Even when dates appeared to match, the row was not deleted. May be it was because I was trying to look up a string in a datetime column.

Thanks,

 

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
Top Experts
User Count
sbeadle
Sisko sbeadle Sisko
1
BevanWeiss
Admiral BevanWeiss
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric