Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • SCADA & Telemetry Solutions
  • :
  • Geo SCADA Expert Forum
  • :
  • Re: Structured Text SQL Query with Direct Variable filter
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51101members
Join Now
245184posts
Join Now

Structured Text SQL Query with Direct Variable filter

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Geo SCADA Expert Forum
Solved
Hardin4019
Lieutenant Hardin4019
Lieutenant
‎2020-10-09 12:49 PM
0 Likes
3
506
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-09 12:49 PM

Structured Text SQL Query with Direct Variable filter

I'm trying to make life a little easier on myself. I have a Mimic with some fields to enter information about a meter template. In particular this meter template doesn't have its own Outstation/Scanner, (this template is for a second, third, or forth meter run). I want to fill in a field "ScannerParentGroupName" that is a String type Variable that I want to use to filter a query in my structured text program that I will setup to fill in the ScannerID field for the points in the template. I have structured text program below, but for some reason, the program upon execution will ask you what value should be assigned to "Scan" since it is a VAR_INPUT. Moving the Scan := ScannerParentGroupName; up before the query doesn't work, and changing the VAR_INPUT to VAR doesn't work. What am I missing?

 

Code;

 

TYPE

SCANNER : DATABASE_OBJECT(TfScanner)
ID: STRING;
FULLNAME: STRING;
END_DATABASE_OBJECT;

END_TYPE

 

PROGRAM TEST

VAR_INPUT
Scan:STRING;
END_VAR

VAR
NEWSTRING AT %M(.New String):STRING;
ScannerParentGroupName AT %I(.Scanner Parent Group Name):STRING;
END_VAR

VAR NOCACHE
Os AT %S(SELECT Id, ID AS SCANNNERID, FULLNAME FROM TfScanner WHERE FULLNAME LIKE ?) : RESULTSET OF SCANNER WITH_PARAMS Scan;
END_VAR
Scan := ScannerParentGroupName;
NEWSTRING := Os.Value.ID;

END_PROGRAM

Solved! Go to Solution.

Labels
  • Logic
  • SCADA
Tags (13)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA control
  • SCADA data
  • SCADA integration
  • SCADA network
  • SCADA programming
  • SCADA software
  • scada system
  • SCADA tutorial
  • SCADA web application
  • Telemetry and SCADA
Share
Reply

Accepted Solutions
geoffpatton
Lt. Commander geoffpatton
Lt. Commander
‎2020-10-09 01:40 PM
0 Likes
0
504
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-09 01:40 PM

Re: Structured Text SQL Query with Direct Variable filter

I have a ST program that on interval executes just fine, but if I right click on it and select execute then it prompts me for the ParentFolderInput. It was written in version 2010 R1.1

 

I was annoyed by it and thought it should not do that, but at the time I was trying to get the project finished and since it worked on a Interval as I needed it I just moved on and never inquired why it does this.

 

If you use a method button to execute it, you can set it to a null '' (single quote, single quote) for its initial value.

 

Here is what  I did for reference.

PROGRAM MyTextProgram

METHOD
Exec AT %M(.Trigger ST_EA.Execute):STRING;
END_METHOD
VAR
ParentFolder AT %M(..FullName) : STRING;
END_VAR

VAR_INPUT
ParentFolderInput : STRING;
END_VAR

ParentFolderInput := CONCAT(ParentFolder, '.BI.%');

Exec(ParentFolderInput);

END_PROGRAM

See Answer In Context

Tags (13)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA control
  • SCADA data
  • SCADA integration
  • SCADA network
  • SCADA programming
  • SCADA software
  • scada system
  • SCADA tutorial
  • SCADA web application
  • Telemetry and SCADA
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
3 Replies 3
geoffpatton
Lt. Commander geoffpatton
Lt. Commander
‎2020-10-09 01:40 PM
0 Likes
0
505
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-09 01:40 PM

Re: Structured Text SQL Query with Direct Variable filter

I have a ST program that on interval executes just fine, but if I right click on it and select execute then it prompts me for the ParentFolderInput. It was written in version 2010 R1.1

 

I was annoyed by it and thought it should not do that, but at the time I was trying to get the project finished and since it worked on a Interval as I needed it I just moved on and never inquired why it does this.

 

If you use a method button to execute it, you can set it to a null '' (single quote, single quote) for its initial value.

 

Here is what  I did for reference.

PROGRAM MyTextProgram

METHOD
Exec AT %M(.Trigger ST_EA.Execute):STRING;
END_METHOD
VAR
ParentFolder AT %M(..FullName) : STRING;
END_VAR

VAR_INPUT
ParentFolderInput : STRING;
END_VAR

ParentFolderInput := CONCAT(ParentFolder, '.BI.%');

Exec(ParentFolderInput);

END_PROGRAM

See Answer In Context

Tags (13)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA control
  • SCADA data
  • SCADA integration
  • SCADA network
  • SCADA programming
  • SCADA software
  • scada system
  • SCADA tutorial
  • SCADA web application
  • Telemetry and SCADA
Share
Reply
BevanWeiss
Sisko BevanWeiss
Sisko
‎2020-10-09 09:03 PM
0 Likes
1
498
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-09 09:03 PM

Re: Structured Text SQL Query with Direct Variable filter

When calling ST SQL with parameters, I normally end up having two logic routines.

The first just setups what the 'inputs' to the query are going to be, and then calls Execute on the second logic routine passing in the inputs which are then VAR_INPUTs on the second logic routine.

 

This is mostly related to the way that the 'sequence' of ST execution occurs.

The SQL Logic is part of the 'Input' scan, which means that it occurs at the same time as the VAR variables are initialised.. which is why the SQL Params can't be VAR variables, they MUST be VAR_INPUT variables, which are available to the ST logic PRIOR to the ST executing.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (13)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA control
  • SCADA data
  • SCADA integration
  • SCADA network
  • SCADA programming
  • SCADA software
  • scada system
  • SCADA tutorial
  • SCADA web application
  • Telemetry and SCADA
Share
Reply
Hardin4019
Lieutenant Hardin4019
Lieutenant
‎2020-10-10 08:42 AM
0 Likes
0
487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-10 08:42 AM

Re: Structured Text SQL Query with Direct Variable filter

Thanks for taking the time to reply and giving me the direction I needed guys.

Tags (13)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA control
  • SCADA data
  • SCADA integration
  • SCADA network
  • SCADA programming
  • SCADA software
  • scada system
  • SCADA tutorial
  • SCADA web application
  • Telemetry and SCADA
Share
Reply
Top Experts
User Count
sbeadle
Sisko sbeadle Sisko
188
BevanWeiss
Sisko BevanWeiss
52
AdamWoodland
Lt. Commander AdamWoodland Lt. Commander
16
JChamberlain
Lieutenant JChamberlain Lieutenant
16
AndrewScott
Lieutenant AndrewScott
15
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric