  • Redundant GeoSCADA 1 MAIN server, 1 Permanent Standby Server
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51230members
Join Now
245444posts
Join Now

Redundant GeoSCADA 1 MAIN server, 1 Permanent Standby Server

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Geo SCADA Expert Forum
Solved
Oncom
Commander Oncom
Commander
‎2020-01-21 12:58 AM
0 Likes
9
2412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-21 12:58 AM

Redundant GeoSCADA 1 MAIN server, 1 Permanent Standby Server

 

ArchitectureArchitecture

Hi All,

 

I have architecture above. 

- 2 Server, 1 server in control network, and 1 server in office network. and both are connected directly peer to peer. 

- 2 separate network.

 

is it architecture is possible?
I was trying to configure as redundant, but it become a problem when Server B as MAIN

what I want is Server A always as MAIN / Primary. and Server B can synchronize data from Server A and Server B can accessed by Client B.

 

thanks
 😀

Solved! Go to Solution.

Labels
  • Redundancy
  • SCADA
  • Telemetry
Share
Reply

Accepted Solutions
JChamberlain
Lieutenant JChamberlain Lieutenant
Lieutenant
‎2020-01-22 12:46 AM
1 Like
5
2380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-22 12:46 AM

Re: Reundant GeoSCADA without changing MAIN server

You might want to raise this with support, we can help you more effectively in through the correct channels.

 

If you right click the server icon and select Invalid Configuration it will tell you why your configuration is invalid.

 

Use a name or address that doesn't exist at all, rather than one that just doesn't have CS installed. We use ICMP as one component for detecting isolation, it doesn't rely on CS replying. I recommend using 'Dummy' or similar, so someone else who looks at the config in future doesn't think it is a mistake.

 

See below what I think will work for you. I'm not 100% sure what each machine's IP address is, I've assumed:

 

Main (A) is 129.76.3.1

Standby (B) is 129.76.3.3

 

Dummy should be configured for the Main's Standby A and the Dummy's Standby B.MainPartner.JPGStandby.JPGMainPSs.JPG

 

 

 

See Answer In Context

Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
9 Replies 9
sbeadle
Sisko sbeadle Sisko
Sisko
‎2020-01-21 01:02 AM
1 Like
8
2410
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-21 01:02 AM

Re: Reundant GeoSCADA without changing MAIN server

Yes, configure server B as a Permanent-Standby. It will serve data and sync from A, but never go Main.

See this new video for architecture guidance:

https://www.youtube.com/watch?v=lmbMy4jJGX0&list=PLa7UGrWOTyjnPpCJxnTZkdBM_6D70qoKl

Search for Permanent Standby in the F1 help.

 

Share
Reply
JChamberlain
Lieutenant JChamberlain Lieutenant
Lieutenant
‎2020-01-21 08:02 PM
1 Like
7
2392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-21 08:02 PM

Re: Reundant GeoSCADA without changing MAIN server

To have B as a permanent standby you'll have to either install an additional hot standby on the control network side (recommended) or configure the permanent standby so it thinks there are is an additional hot standby - the permanent standby needs to have two hot standby partners configured.


NoName.JPGDummyName.JPG

Share
Reply
Oncom
Commander Oncom
Commander
‎2020-01-22 12:08 AM
0 Likes
6
2385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-22 12:08 AM

Re: Reundant GeoSCADA without changing MAIN server

@sbeadle Hi Steve, thanks for your respond.

in your video, and also mentioned by @JChamberlain the MAIN server should have standby pair. so is it still possible?

image.png

 

 


I was try to configure it but fail. my Permanent standby Server doesn't start: always in state: Starting.. 

I configure Permanent Standby Server as on Manual Help 

SC_OPCSERVER(STANDBY).PNG

 

and here is my configuration on MAIN server:

SC_SCADASERVER(MAIN)_PERMANENT.PNGSC_SCADASERVER(MAIN)_STANDBYTAB.PNG

 

what I was trying in MAIN Server:
-put IP adress of StandbyPC(permanent standby) on Standby A : Permanent standby PC can start but show up Error Invalid configuration, Main Server also show invalid configuration

 

-put IP address of Main PC (this computer IP it self) : Main Server can start as Main, Standby Server always in Starting state

 

-put IP address of other PC (no clearscada) : Main Server can start as Main, Standby Server always in Starting state

Share
Reply
JChamberlain
Lieutenant JChamberlain Lieutenant
Lieutenant
‎2020-01-22 12:46 AM
1 Like
5
2381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-22 12:46 AM

Re: Reundant GeoSCADA without changing MAIN server

You might want to raise this with support, we can help you more effectively in through the correct channels.

 

If you right click the server icon and select Invalid Configuration it will tell you why your configuration is invalid.

 

Use a name or address that doesn't exist at all, rather than one that just doesn't have CS installed. We use ICMP as one component for detecting isolation, it doesn't rely on CS replying. I recommend using 'Dummy' or similar, so someone else who looks at the config in future doesn't think it is a mistake.

 

See below what I think will work for you. I'm not 100% sure what each machine's IP address is, I've assumed:

 

Main (A) is 129.76.3.1

Standby (B) is 129.76.3.3

 

Dummy should be configured for the Main's Standby A and the Dummy's Standby B.MainPartner.JPGStandby.JPGMainPSs.JPG

 

 

 

See Answer In Context

Share
Reply
Oncom
Commander Oncom
Commander
‎2020-01-26 10:16 PM
0 Likes
3
2323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-26 10:16 PM

Re: Reundant GeoSCADA without changing MAIN server

@JChamberlain Hi,

 

I was try again using that configuration from you. but still the Standby doesn't want to Start, the state always: Starting..

already change the port too in permanent standby tab to 5482, and still didn't work

 

BTW, to raise this with support, do we need to have support/CF? or just simply email to Trss-support@se.com or your email 😉?

 

 

Thanks

Share
Reply
BevanWeiss
Sisko BevanWeiss
Sisko
‎2020-01-26 10:30 PM
0 Likes
2
2320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-26 10:30 PM

Re: Reundant GeoSCADA without changing MAIN server

When you ping the Primary Server IP address from the Permanent Standby server what result do you get?

If that doesn't work, then you need to fix that issue.

 

If that does work, then you should try TCPing (or telnet) to the default port 5481 to ensure that this works.  If it doesn't, then you likely have a firewall problem.

 

The IP addresses that you have listed seem a little unusual based upon the first image that you have suggested.

I would have expected that you would be using link local addresses for the direct link between the two servers (Primary and Permanent Standby), and hence would have 169.254.x.y format IP addresses.  You could allocate a Class A, B or C private IP address (or even technically a public IP address) to these interfaces, but it seems wasteful if they will only be used to link these two computers together for the ClearSCADA data replication.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
Oncom
Commander Oncom
Commander
‎2020-01-26 11:05 PM
0 Likes
1
2317
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-26 11:05 PM

Re: Reundant GeoSCADA without changing MAIN server

hi @BevanWeiss ,

 

I can ping from each others, and firewall has been disabled on both side. I already successful configure it as Redundant pairs. that 5481 port should be OK then.

 

Yes this is unusual Class B IP address using public IP, I already mentioned it to them (my customer) to use private IP as a standard.

and the link between computers is only connected each others for data replication.

Share
Reply
BevanWeiss
Sisko BevanWeiss
Sisko
‎2020-01-26 11:21 PM
0 Likes
0
2314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-26 11:21 PM

Re: Reundant GeoSCADA without changing MAIN server

I would recommend leaving all ports as default 5481.

 

If you have already successfully configured the servers as redundant pairing, then you should just need to go to the Permanent Standby, and change the mode on this server (the Permanent Standby) from Hot-Standby Pair, to Permanent Standby, and things should work.  If it complains about wanting a Standby B address just enter 0.0.0.0 for this.

 

You will absolutely need to have the Primary Server running first, for the Permanent Standby to transition from Starting to Synchronising. And then once Synchronised it should just run as Permanent Standby from that point until the Primary Server is lost, in which case it will revert to Starting (until Re-synchronisation can occur again).

 

To get official tech support, you would need to have a Site ID that is in support (technically all sites that you are involved with should be within support).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
Oncom
Commander Oncom
Commander
‎2020-01-28 10:55 PM
0 Likes
0
2291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-28 10:55 PM

Re: Reundant GeoSCADA without changing MAIN server

now it works after I restart all PC and still using this configuration from @JChamberlain .

 

Thanks All, @JChamberlain @BevanWeiss @sbeadle 

Share
Reply
Top Experts
User Count
sbeadle
Sisko sbeadle Sisko
188
BevanWeiss
Sisko BevanWeiss
52
AdamWoodland
Lt. Commander AdamWoodland Lt. Commander
16
JChamberlain
Lieutenant JChamberlain Lieutenant
16
AndrewScott
Lieutenant AndrewScott
15
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric