Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • SCADA & Telemetry Solutions
  • :
  • Geo SCADA Expert Forum
  • :
  • Re: Querying Alarm Severity settings across an entire database
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49246members
Join Now
242459posts
Join Now

Querying Alarm Severity settings across an entire database

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Geo SCADA Expert Forum
Solved
rlao
Ensign rlao
Ensign
‎2020-02-19 10:11 PM
0 Likes
7
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-19 10:11 PM

Querying Alarm Severity settings across an entire database

Hi all,

 

Broad question, but I am undertaking some alarm rationalization work and am wondering if there is an efficient way to query what the value of all alarm severity fields are across all relevant object classes in a ClearSCADA database?

 

The only way I know of currently is to individually query object classes like CeNetAnalog, CPointAlg, etc. one by one for all of their alarm severity fields and manually compile all the information somewhere like a spreadsheet. Quite a time-consuming process and my main concern is that it is very easy to accidentally miss alarms on object types that I'm not aware even had configurable alarms in the first place. For example, I only just learnt that CRootGroup has a WSEventSeverity field for workstation events as well as multiple aggregates that each have severity settings too.

 

I'm just thinking could there be a way to work backwards instead and somehow start from the severity settings in Server Config and somehow grab a list of all references to that?

Solved! Go to Solution.

Labels
  • SCADA
Share
Reply

Accepted Solutions
sbeadle
Sisko sbeadle Sisko
Sisko
‎2020-02-24 03:27 AM
0 Likes
1
1359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-24 03:27 AM

Re: Querying Alarm Severity settings across an entire database

There's a variable number of severities per object. Here is a 'meta query' you can use to find severity data:

 

SELECT
	'select ''' || TABLE || ''',''' || NAME || ''',T.Id, T.FullName, T.' || NAME || ',S.Description from ' || TABLE || ' T left join CSeverity S on T.' || NAME || ' = S.Priority ' AS SQL
FROM
	DBFIELDDEF
WHERE
	NAME LIKE '%Severity' AND SIZE = 1 AND TYPE = 1

 

The output is a longish list of queries for each database type.

 

See Answer In Context

Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
7 Replies 7
Hardin4019
Lieutenant Hardin4019
Lieutenant
‎2020-02-20 06:13 AM
0 Likes
0
1395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-20 06:13 AM

Re: Querying Alarm Severity settings across an entire database

Maybe not the most efficient way, but the way I did something like this was:

 

Make a mimic with separate list of Modbus Digitals, Modbus Analogs, OPC Digitals, OPC Analogs, Internal Digitals, Internal Analogs, etc, each with all of the alarm fields to the point that I was happy that I had everything I wanted.

 

Then I copied the Query from each list in to its own SQL Export object and gave each export a unique Output file name. Now whenever someone asks me for the alarm details, all I need to do is execute each SQL Export and copy the files from the server to an email. 

Share
Reply
AdamWoodland
Lt. Commander AdamWoodland Lt. Commander
Lt. Commander
‎2020-02-20 02:01 PM
0 Likes
4
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-20 02:01 PM

Re: Querying Alarm Severity settings across an entire database

No simple way, typically I do what you propose and query each table and union them all together. I once tried to write a program to find all fields call "Severity" and auto generate some SQL but I don't think I ever finished it.

 

The way the ClearSCADA database is structured does make some thing much easier... however in cases such as this it can be unhelpful.

Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-02-20 02:19 PM
0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-20 02:19 PM

Re: Querying Alarm Severity settings across an entire database

It almost needs a feature request for a summary table of 'Alarm Severity '.. not that this would help in many situations.

Alarm redirections can often make the actual object configured severity meaningless.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
rlao
Ensign rlao
Ensign
‎2020-02-20 03:18 PM
0 Likes
2
1376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-20 03:18 PM

Re: Querying Alarm Severity settings across an entire database

Thanks for confirming Adam. At least it sounds like I'm on the right track with how I'm approaching this and not missing something obvious. Some sort of Alarm Severity Summary table as Bevan suggested would be very helpful, although I'm not exactly sure how feasible it is to implement such a feature.

Share
Reply
sbeadle
Sisko sbeadle Sisko
Sisko
‎2020-02-24 03:27 AM
0 Likes
1
1360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-24 03:27 AM

Re: Querying Alarm Severity settings across an entire database

There's a variable number of severities per object. Here is a 'meta query' you can use to find severity data:

 

SELECT
	'select ''' || TABLE || ''',''' || NAME || ''',T.Id, T.FullName, T.' || NAME || ',S.Description from ' || TABLE || ' T left join CSeverity S on T.' || NAME || ' = S.Priority ' AS SQL
FROM
	DBFIELDDEF
WHERE
	NAME LIKE '%Severity' AND SIZE = 1 AND TYPE = 1

 

The output is a longish list of queries for each database type.

 

See Answer In Context

Share
Reply
tfranklin
Lieutenant tfranklin
Lieutenant
‎2020-02-24 07:07 AM
0 Likes
0
1353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-24 07:07 AM

Re: Querying Alarm Severity settings across an entire database

This sounds like a really nice opportunity to ask for a feature request to do something like SQL Views but within the CS database. Additionally, server-side cached query objects would be really nice as well. 

 

Constantly having to union together OPC stuff isn't a big deal but gets repetitive to type out. 

 

For cached queries, have a query object (like the ones for GIS) that runs the query every x seconds/minutes and caches the result set.  Users can query those objects like they would a view and get the results directly from cache rather than having the server re-query it.  This could alleviate a big load when you have a server that runs a large number of clients.  Having something in there properties where it logs access count from client vs scheduled and stops running if the access count from clients doesn't increase after x minutes would also alleviate unnecessary runs. 

 

I've been trying to find ways to utilize the query objects for GIS stuff in a way that was not intended and I've yet to find a use outside of just storing common queries on them.

Share
Reply
rlao
Ensign rlao
Ensign
‎2020-03-02 03:41 PM
0 Likes
0
1295
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-02 03:41 PM

Re: Querying Alarm Severity settings across an entire database

Thanks Steve, I got around to trying your meta-query and it helped considerably. It needed a little bit of tweaking, mainly around all the aggregate classes as they need their select statements manually modified to inner join on CDBObject (as they don't directly contain a FullName).

Share
Reply
Top Experts
User Count
sbeadle
Sisko sbeadle Sisko
1
geoffpatton
Lieutenant geoffpatton
1
BevanWeiss
Admiral BevanWeiss
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric