New in the Community? Get started here

Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Geo SCADA Expert Forum
Make the most of your remote operations with end-to-end solutions with Process Automation’s SCADA and Telemetry Solutions. With the challenges that remote sites present, reliable communications for remote operation, monitoring & management are vital in enhancing productivity and ensuring profitability.
cancel
Showing results for 
Show  only  | Search instead for 
Did you mean: 
Crewman

OPC ParentGroupName property empty after update 2017R3

After update to 2017R3 “November 2019 update” (6.80.7285.2) the OPC "ParentGroupName" property is empty.

We are using this property in application scripts. After update these scripts fail.
Anyone familiar with this problem?

5 REPLIES 5
Highlighted
Ensign

Re: OPC ParentGroupName property empty after update 2017R3

This issue has just been fixed earlier today and the fix will be included in the January 2020 monthly updates.


Andrew Scott, Lead Engineer, AVEVA
Crewman

Re: OPC ParentGroupName property empty after update 2017R3

OK, thanks Andrew for your quick response.

Sisko

Re: OPC ParentGroupName property empty after update 2017R3

A potential workaround is to use the two dots on a relative reference to refer to a parent item.

e.g. "..FullName" is equivalent to ".ParentGroupName"

 

Crewman

Re: OPC ParentGroupName property empty after update 2017R3

Hello Stephen,

 

Thanks for thinking along with us.

 

We use the field “ParentGroupName” in global scripts with query’s something like

 

sSQL = "SELECT FullName FROM CMimic WHERE ParentGroupName = '" & GroepFN & "' AND UPPER(Name) LIKE......

 

It’s a lot of work for us to change that and use the relative reference,

We will wait for the monthly update.

 

Kind regards, Kees

Crewman

Re: OPC ParentGroupName property empty after update 2017R3

For scripts you can use the PARENTGROUPID:

  • A.PARENTGROUPNAME.... => A.PARENTGROUPID->FULLNAME....