Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • SCADA & Telemetry Solutions
  • :
  • Geo SCADA Expert Forum
  • :
  • Re: Is Server.SetOPCValue with DPN3 pulse point through Script supported?
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49613members
Join Now
242991posts
Join Now

Is Server.SetOPCValue with DPN3 pulse point through Script supported?

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Geo SCADA Expert Forum
Solved
Tanquen
Lt. Commander Tanquen
Lt. Commander
‎2020-08-25 12:37 PM
0 Likes
3
401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-25 12:37 PM

Is Server.SetOPCValue with DPN3 pulse point through Script supported?

I need to have a button write or set off two different DNP3 Pulse tags.

 

This gives the error, "The Value is read only and may not be written to."

 

Server.SetOPCValue "...Tags DNP.Control.Download Setpoints CMD", ''Download''

 

 

This PickParam has no errors when selected:

 

PickType 5

PickParam ""...Tags DNP.Control.Download Setpoints CMD.ObjectLink"+'?Control&Action=''Download'''"

 

This works with an internal tag:

 

Server.SetOPCValue "...Tags DNP.Control.Test1", 1

Solved! Go to Solution.

Tags (1)
  • Tags:
  • english
Share
Reply

Accepted Solutions
geoffpatton
Lieutenant geoffpatton
Lieutenant
‎2020-08-27 06:56 AM
0 Likes
2
378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-27 06:56 AM

Re: Is Server.SetOPCValue with DPN3 pulse point through Script supported?

No you have to set and variable equal to your point's full name and then do an interface control on it.

With a Pulse Null you write a 0

With a Pulse Trip you write a 0 for the first action and a 1 for the second one.

 

Option Explicit
Sub OpenBreaker()
dim objOpenCmd
'Create a reference to the Open Object.
Set objOpenCmd = Server.FindObject(Server.GetOPCValue("...IO.Control.Open CMD.Fullname"))

objOpenCmd.Interface.Control 0

End Sub

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
geoffpatton
Lieutenant geoffpatton
Lieutenant
‎2020-08-27 01:10 PM
0 Likes
0
365
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-27 01:10 PM

Re: Is Server.SetOPCValue with DPN3 pulse point through Script supported?

Option Explicit is not required it is extremely useful when writing or editing the code. It generates an error if you forgot to declared variables that you use in your routine, or you misspelled a variable.

 

If you are using a code fragment in a pick action you don't need Sub lines, but you do in the mimic scripting.

 

Your question about weather the sub line were necessary made me think a moment. I don't use the code fragment option much and I tend to forget about it. My scripts are almost always more complicated than I want to try to put in a code fragment. Most of mine check if the user has control privileges and if they do not it prompts them that they don't have the right to operate the button and need to use a different login. Most of mine also ask to confirm they meant to press the button to prevent accidental operations.

 

Also you can run debugging on the code in the Mimic script section.

 

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
3 Replies 3
geoffpatton
Lieutenant geoffpatton
Lieutenant
‎2020-08-27 06:56 AM
0 Likes
2
379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-27 06:56 AM

Re: Is Server.SetOPCValue with DPN3 pulse point through Script supported?

No you have to set and variable equal to your point's full name and then do an interface control on it.

With a Pulse Null you write a 0

With a Pulse Trip you write a 0 for the first action and a 1 for the second one.

 

Option Explicit
Sub OpenBreaker()
dim objOpenCmd
'Create a reference to the Open Object.
Set objOpenCmd = Server.FindObject(Server.GetOPCValue("...IO.Control.Open CMD.Fullname"))

objOpenCmd.Interface.Control 0

End Sub

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Tanquen
Lt. Commander Tanquen
Lt. Commander
‎2020-08-27 12:35 PM
0 Likes
1
368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-27 12:35 PM

Re: Is Server.SetOPCValue with DPN3 pulse point through Script supported?

I had to fix my PickParam and add the “.ObjectLink” on the end. When they use the built in method or the PickParam Animation Expression they always pass the DNP3 pulse description. I'm not sure why they do but it works. The "objRefreshCmd.Interface.Control" will not take a string but it seems to work the same.

 

I’m using it in a Pick Action Execute Code Fragment so I can removed the Sub or call it at the end to get it to run. Any reason to keep the Option Explicit and Sub lines?

 

 

Option Explicit
Sub Refresh()


dim objRefreshCmd
dim objDownloadCmd
'Create a reference to the Refresh and Download objects.
Set objRefreshCmd= Server.FindObject(Server.GetOPCValue("...Tags DNP.Control.Refresh Setpoints CMD.Fullname"))
Set objDownloadCmd = Server.FindObject(Server.GetOPCValue("...Tags DNP.Control.Download Setpoints CMD.Fullname"))

 

objRefreshCmd.Interface.Control 0
objDownloadCmd.Interface.Control 0

 

End Sub

 

Refresh

Tags (1)
  • Tags:
  • english
Share
Reply
geoffpatton
Lieutenant geoffpatton
Lieutenant
‎2020-08-27 01:10 PM
0 Likes
0
366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-27 01:10 PM

Re: Is Server.SetOPCValue with DPN3 pulse point through Script supported?

Option Explicit is not required it is extremely useful when writing or editing the code. It generates an error if you forgot to declared variables that you use in your routine, or you misspelled a variable.

 

If you are using a code fragment in a pick action you don't need Sub lines, but you do in the mimic scripting.

 

Your question about weather the sub line were necessary made me think a moment. I don't use the code fragment option much and I tend to forget about it. My scripts are almost always more complicated than I want to try to put in a code fragment. Most of mine check if the user has control privileges and if they do not it prompts them that they don't have the right to operate the button and need to use a different login. Most of mine also ask to confirm they meant to press the button to prevent accidental operations.

 

Also you can run debugging on the code in the Mimic script section.

 

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
BevanWeiss
Admiral BevanWeiss
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric