Sign In Help
Schneider Electric
HelpLogin / Register

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Communities
  • :
  • SCADA & Telemetry Solutions
  • :
  • Geo SCADA Expert Forum
  • :
  • Re: Importing Historic Data
Community Menu
  • Forums
    • By Topic
        • EcoStruxure Building
          • Field Devices Forum
        • EcoStruxure Power & Grid
          • Metering & Power Quality
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Automation Forum
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
          • Motorabgangstechnik & Antriebstechnik Forum
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Solutions for Motor Management
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
          • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
        • Power Distribution NEMA
          • US Utility Forum
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure Building
        • Field Devices Forum
      • EcoStruxure Power & Grid
        • Metering & Power Quality
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Automation Forum
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
        • Motorabgangstechnik & Antriebstechnik Forum
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Solutions for Motor Management
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
        • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Power Distribution NEMA
        • US Utility Forum
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • EcoStruxure Power & Grid
          • Backstage Access Resources
        • Industrial Automation
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
          • UK&I Residential and Commercial Electrical Distribution
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
          • Solutions for eMobility
          • Digital Hospital Solutions – UK&I
        • Knowledge Center
          • Industrial Automation How-to videos
          • Digital E-books
          • Success Stories Corner
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
        • Retail
          • Solutions for eMobility
        • Retail
          • Digital Hospital Solutions – UK&I
      • EcoStruxure Power & Grid
        • Backstage Access Resources
      • Industrial Automation
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
        • UK&I Residential and Commercial Electrical Distribution
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
        • Solutions for eMobility
        • Digital Hospital Solutions – UK&I
      • Knowledge Center
        • Industrial Automation How-to videos
        • Digital E-books
        • Success Stories Corner
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
      • Retail
        • Solutions for eMobility
      • Retail
        • Digital Hospital Solutions – UK&I
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Register Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
53122members
248564posts

Importing Historic Data

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Geo SCADA Expert Forum
Solved
DavidSkilbeck
Lt. Commander DavidSkilbeck
Lt. Commander
‎2021-02-23 12:31 AM
0 Likes
11
546
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-23 12:31 AM

Importing Historic Data

Hi, I have been running through the article below.

 

https://tprojects.schneider-electric.com/GeoSCADAHelp/Geo%20SCADA%202020/Content/ServerAdministratio...

 

For the last example 2.

Initially used the data provided as below

2016,07,03,16,23,23,0

2016,07,03,16,24,23,12

and got a message below

ErrorMessageCSVImport.png

I changed the data to below to get it to work

(earliest I could go back).

2021,02,22,16,11,38,000,4.0218887
2021,02,22,16,11,53,000,3.1718216
.......
It did work, however the date in the history was today's date and not that of the file.
ErrorMessageCSV2Import.png

 

Is there a way of adjusting the time window (and if so how far back can we go).
Is there a setting for the correct date / time  to be loaded in to the history, as to that of the file ( I notice there is AM listed).

Thanks,

Labels
  • SCADA
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply

Accepted Solutions
AndrewScott
Lt. Commander AndrewScott
Lt. Commander
‎2021-02-23 01:58 AM
0 Likes
10
541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-23 01:58 AM

Re: Importing Historic Data

The writable life for historic data is configured using the Server Configuration tool:

https://tprojects.schneider-electric.com/GeoSCADAHelp/Geo%20SCADA%202020/Default.htm#ServerAdministr... l

 

The timestamps in the CSV file are in UTC, but ViewX is displaying the times in local time of the client PC, which appears to be UTC+10:00, so you are probably located in Australia.


Andrew Scott, Lead Engineer, AVEVA

See Answer In Context

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
11 Replies 11
AndrewScott
Lt. Commander AndrewScott
Lt. Commander
‎2021-02-23 01:58 AM
0 Likes
10
542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-23 01:58 AM

Re: Importing Historic Data

The writable life for historic data is configured using the Server Configuration tool:

https://tprojects.schneider-electric.com/GeoSCADAHelp/Geo%20SCADA%202020/Default.htm#ServerAdministr... l

 

The timestamps in the CSV file are in UTC, but ViewX is displaying the times in local time of the client PC, which appears to be UTC+10:00, so you are probably located in Australia.


Andrew Scott, Lead Engineer, AVEVA

See Answer In Context

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
DavidSkilbeck
Lt. Commander DavidSkilbeck
Lt. Commander
‎2021-02-23 01:14 PM
0 Likes
9
527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-23 01:14 PM

Re: Importing Historic Data

Hi, do you refer to this section as below

 

ErrorMessageCSV3Import.png

 

as it seems to be set to 520 weeks.

I figures it would be something about UTC / Local.

Thanks,

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
BevanWeiss
Sisko BevanWeiss
Sisko
‎2021-02-23 02:37 PM
0 Likes
8
520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-23 02:37 PM

Re: Importing Historic Data

Those sections that you have indicated only apply to 'Synchronisation Data'.. not to the data that the Main server is actively able to write to.

 

The section that applies for the historical writes is at the top.  If you look at the help for 'Archive after' you will see that this is what triggered the inability to update/add new historical data.

 

The help comments are:

Define the Archive Time for Historic Data

Alarm Summary, Configuration Changes Auditing, Event Journal or Historic Data is stored online for a specified duration (see Specify the Duration to Retain Historic Data Online), then the data is deleted. You can define a period of time after, which data that is stored online can be archived. When historic data is marked as eligible for archiving, it can be archived for example to CD, DVD and so on, (it has to be archived before the duration of the online data expires).

During the period that data is stored online, the data can be altered (by having new values reported for the time period) unless it is marked as eligible for archiving. When historic data is marked as eligible for archiving, it can no longer be altered on the disk—the new records for that period / time cannot be written to; it can only be read.

 

2021-02-24 09_18_57-Clipboard.png

 

The concept here is that once you say that a historical period is 'archivable' then it should no longer be modified.  Since it may no longer be on the computer itself, and may actually be on a CD / DVD or write-once media stored for archiving.

 

For some reason I always 'think' that having an archive after time configured will help performance.  But I'm pretty sure it doesn't.  It obviously cuts down on when re-indexing might be required, but if you're trying to insert historical data into your system, then you probably need that historical data in there, and the cost of indexing is just a burden you need to wear.  As such, I'd say for 'most' systems, probably not having the Archive after tick box ticked is a reasonable approach (I think the default is ticked and 2 weeks).  If you will archive off to DVD etc, then you will need to have this configured.  But Geo SCADA Expert archiving is a little confusing anyway... so I suspect most people aren't using it.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
geoffpatton
Lt. Commander geoffpatton
Lt. Commander
‎2021-02-24 06:22 AM
0 Likes
7
509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-24 06:22 AM

Re: Importing Historic Data

I have always kept years of history, but never actually archived any of it.

If I am remembering correctly the Archive after setting helps when you have redundancy and are restarting one of the machines.

This could have changed over the years too. I have been using ClearSCADA since version 2005.

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
BevanWeiss
Sisko BevanWeiss
Sisko
‎2021-02-24 02:53 PM
0 Likes
6
485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-24 02:53 PM

Re: Importing Historic Data

I think this behaviour might have changed in recent versions.

I did a sync yesterday, and having the 4 week 'archive after' setting did NOT help in any way... the full 4 months of historic data was synchronised... which was quite painful over the two tin cans, and low value twine used for the inter-server connection.

 

I would have hoped that it would have done a hash over the current data blocks, and only requested sync where the data block hash didn't match... but it seems that's not the case either (or the behaviour is buggy..)


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
AdamWoodland
Commander AdamWoodland Commander
Commander
‎2021-02-24 03:05 PM
1 Like
4
482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-24 03:05 PM

Re: Importing Historic Data

I think the methodology of how far back it syncs was changed around 2017 R1, based on the earlier change...

 

> would have done a hash

 

It used to do a CRC comparison up to 2013R1 or R2, they changed it as the CRC was too intensive to a much faster size and last modified date. If those match it doesn't re-sync the file.

 

Does cause problems if you copy/restore files to a server and that copy changes the last modified date, as the resync will just resync everything anyway.

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
geoffpatton
Lt. Commander geoffpatton
Lt. Commander
‎2021-02-24 03:27 PM
0 Likes
0
480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-24 03:27 PM

Re: Importing Historic Data

Good to know, I like your networking description. I think all of the servers I work on have lots of resources and a good gigabit connection between them, and I rarely am the one that restarts one.

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
BevanWeiss
Sisko BevanWeiss
Sisko
‎2021-02-24 06:39 PM
0 Likes
3
470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-24 06:39 PM

Re: Importing Historic Data

Hmm... thanks for the refresher on that new system @AdamWoodland .  Unfortunately doesn't match my experience from yesterday.

 

The primary server had only been off since the 20th Feb, so it should have only been missing 4 days worth of data (or the last 1 week granules needing sync).  But it definitely resynchronised the whole history.

 

I do have a scheduled historic optimise, but that's only every Sunday... I guess I'll need to keep an eye on it, and report if it happens again.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
DavidSkilbeck
Lt. Commander DavidSkilbeck
Lt. Commander
‎2021-02-25 09:02 PM
0 Likes
2
435
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-25 09:02 PM

Re: Importing Historic Data

Hi, these are the settings for my Geo SCADA.

 

ErrorMessageCSV4Import.png

This a sample of the data I want to import
4.0218887,2020,07,22,16,11,38,010,192,8
3.1718216,2020,07,22,16,11,53,010,192,8

This is what I am getting in Geo SCADA

ErrorMessageCSV5Import.png

If I use the below it wont import historic values

dt = new DateTime(2020, 2, 26, 11, 55, 52);

If I change the 2020 to 2021 it works.

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
DavidSkilbeck
Lt. Commander DavidSkilbeck
Lt. Commander
‎2021-02-28 06:19 PM
0 Likes
1
403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-28 06:19 PM

Re: Importing Historic Data

It has been working. I just needed to select last year for it to display.

Even with offset property for the point set to "Hour - 2 Years", yo have to change search to last year.

Thanks,

 

Share
Reply
BevanWeiss
Sisko BevanWeiss
Sisko
‎2021-02-28 09:00 PM
0 Likes
0
394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-28 09:00 PM

Re: Importing Historic Data

It's possible that there are bugs around the offset property (and just Historic List behaviour in certain scenarios).

It would be worth reviewing the help documentation, and if you see behaviour that differs from the help documentation then raising a case with Tech Support.  That way they know about it, and can get it fixed for the future.

 

But always good to double check what the actual query is being used for the lists.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
Top Experts
User Count
sbeadle
Sisko sbeadle Sisko
188
BevanWeiss
Sisko BevanWeiss
56
AndrewScott
Lt. Commander AndrewScott
18
AdamWoodland
Commander AdamWoodland Commander
17
JChamberlain
Lt. Commander JChamberlain Lt. Commander
16
geoffpatton
Lt. Commander geoffpatton
10
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2021, Schneider Electric