Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • SCADA & Telemetry Solutions
  • :
  • Geo SCADA Expert Forum
  • :
  • [Imported] ScxV6Server.Connect error "SetClientDetails Failed"
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51304members
Join Now
245511posts
Join Now

[Imported] ScxV6Server.Connect error "SetClientDetails Failed"

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Geo SCADA Expert Forum
Solved
sbeadle
Sisko sbeadle Sisko
Sisko
‎2019-11-07 03:43 AM
0 Likes
1
486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-11-07 03:43 AM

[Imported] ScxV6Server.Connect error "SetClientDetails Failed"

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: nminchin, originally posted: 2019-08-20 08:08:29 Id:487
Hi,

I have an excel tool that we've been using for years to do bulk changes, but recently trying it in ClearSCADA 2017, I'm getting this error when attempting to simply connect to the ScxV6Server object.

`SetClientDetails Failed`

I can't find any info on this error anywhere, any ideas?

Solved! Go to Solution.

Labels
  • SCADA
Share
Reply

Accepted Solutions
sbeadle
Sisko sbeadle Sisko
Sisko
‎2019-11-07 03:44 AM
0 Likes
0
485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-11-07 03:44 AM

Re: [Imported] ScxV6Server.Connect error "SetClientDetails Failed"

>>Responses imported from previous forum


Reply From User: nminchin, posted: 2019-08-20 22:18:03
Hmm, I can't edit my OP... I just wanted to clarify:
The error occurs on this line
`ScxV6Server.Connect(system, user, pass)`
Where the 3 arguments are actual values for my live running system.

 

Reply From User: JesseChamberlain, posted: 2019-08-21 04:09:27
Check the DB log, it should give you something more descriptive.

There will be SetClientDetails( IN: and SetClientDetails( OUT: lines with the actual parameters and the result.


Reply From User: nminchin, posted: 2019-08-21 04:41:40
Thanks Jesse.

I've attached what I think are the relevant lines, but not sure..

```
21-AUG-2019 04:36:03.143 1188 [SVR] Accepted connection 7 from 127.0.0.1:49812 to 127.0.0.1:5481 on socket 0xa38...
21-AUG-2019 04:36:03.143 1188 [SVR] ... Connection 7: Type 1, client version 0x64F1A29 (6.79.6697), (Uncompressed,Floating License,Include Checksums)
21-AUG-2019 04:36:03.143 1188 [SVR] ... Connection 7: confirmed, link version 6.79.6697, client name 'IP 127.0.0.1, Session 1'
21-AUG-2019 04:36:03.143 1188 [SCX] Server link attached to socket 0xa38
21-AUG-2019 04:36:03.143 1188 [SCX] Unconnected dedicated link requested, creating new parent link (Id = 97)
21-AUG-2019 04:36:03.143 1188 [PL97] Creating dedicated link
21-AUG-2019 04:36:03.143 1188 [PL97] Attaching to socket 0xa38
21-AUG-2019 04:36:03.143 1188 [SVRTHR] 1 AddClient from 127.0.0.1:49812, link is [SCX] 1:15
21-AUG-2019 04:36:03.143 1188 [SCX] 1:15 QP Created
21-AUG-2019 04:36:03.143 052C [SCX] 1:15 InitSecureSession( IN: )
21-AUG-2019 04:36:03.143 052C [SCX] 1:15 Found matching certificate for connection to local IP address 127.0.0.1
21-AUG-2019 04:36:03.143 052C [SCX] 1:15 InitSecureSession( OUT: hr 0 - Ok. )
21-AUG-2019 04:36:03.144 052C [SCX] 1:15 StartSecureSession( IN: )
21-AUG-2019 04:36:03.144 052C [SCX] 1:15 StartSecureSession( OUT: hr 0 - Ok. )
21-AUG-2019 04:36:03.144 0F10 [SCX] 1:15 Entering secure session
21-AUG-2019 04:36:03.144 052C [SCX] 1:15 SetClientDetails( IN: LoggedOn 0, IsLocal 0, User "", Workstation Name "", Client Name "Unknown" )
21-AUG-2019 04:36:03.144 052C [SCX] 1:15 SetClientDetails( OUT: Hr 0 - Ok. )
```

Also attached the file itself.

Cheers!

Attached file: (editor/qs/2moj3739m9y9.log), DB_001 (1).log File size: 839986


Reply From User: JesseChamberlain, posted: 2019-08-22 01:57:48
That does look like the relevant lines. Here's what it looks like when I do it:

22-AUG-2019 00:11:52.355 0374 [SCX] 8:08 QP Created
22-AUG-2019 00:11:52.355 29CC [SCX] 8:08 InitSecureSession( IN: )
22-AUG-2019 00:11:52.356 29CC [SCX] 8:08 Found matching certificate for connection to local IP address 127.0.0.1
22-AUG-2019 00:11:52.356 29CC [SCX] 8:08 InitSecureSession( OUT: hr 0 - Ok. )
22-AUG-2019 00:11:52.356 29CC [SCX] 8:08 StartSecureSession( IN: )
22-AUG-2019 00:11:52.356 29CC [SCX] 8:08 StartSecureSession( OUT: hr 0 - Ok. )
22-AUG-2019 00:11:52.356 0AD8 [SCX] 8:08 Entering secure session
22-AUG-2019 00:11:52.357 29CC [SCX] 8:08 SetClientDetails( IN: LoggedOn 0, IsLocal 0, User "", Workstation Name "", Client Name "Unknown" )
22-AUG-2019 00:11:52.357 29CC [SCX] 8:08 SetClientDetails( OUT: Hr 0 - Ok. )
22-AUG-2019 00:11:52.357 0AD8 [SCX] 8:08 SetClientDetails( IN: Lcid 0xFFFFFFFF, ClientName WTAULVSE0C7BFPL::ScxV6Server )
22-AUG-2019 00:11:52.357 0AD8 [SCX] 8:08 SetClientDetails( OUT: Features 0x8C0F, hr 0 - Ok. )
22-AUG-2019 00:11:52.357 0AD8 [SCX] 8:08 AdviseState( IN: )
22-AUG-2019 00:11:52.357 0AD8 [SCX] 8:08 AdviseState( OUT: hr 0 - Ok. )
22-AUG-2019 00:11:52.360 0AD8 [SCX] 8:08 Advise( IN: Port 5503, ClientId 2 )

So it seems to not be doing the second SetClientDetails for some reason...

If you'd like us to look at it further please raise a support ticket.

See Answer In Context

Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
1 Reply 1
sbeadle
Sisko sbeadle Sisko
Sisko
‎2019-11-07 03:44 AM
0 Likes
0
486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-11-07 03:44 AM

Re: [Imported] ScxV6Server.Connect error "SetClientDetails Failed"

>>Responses imported from previous forum


Reply From User: nminchin, posted: 2019-08-20 22:18:03
Hmm, I can't edit my OP... I just wanted to clarify:
The error occurs on this line
`ScxV6Server.Connect(system, user, pass)`
Where the 3 arguments are actual values for my live running system.

 

Reply From User: JesseChamberlain, posted: 2019-08-21 04:09:27
Check the DB log, it should give you something more descriptive.

There will be SetClientDetails( IN: and SetClientDetails( OUT: lines with the actual parameters and the result.


Reply From User: nminchin, posted: 2019-08-21 04:41:40
Thanks Jesse.

I've attached what I think are the relevant lines, but not sure..

```
21-AUG-2019 04:36:03.143 1188 [SVR] Accepted connection 7 from 127.0.0.1:49812 to 127.0.0.1:5481 on socket 0xa38...
21-AUG-2019 04:36:03.143 1188 [SVR] ... Connection 7: Type 1, client version 0x64F1A29 (6.79.6697), (Uncompressed,Floating License,Include Checksums)
21-AUG-2019 04:36:03.143 1188 [SVR] ... Connection 7: confirmed, link version 6.79.6697, client name 'IP 127.0.0.1, Session 1'
21-AUG-2019 04:36:03.143 1188 [SCX] Server link attached to socket 0xa38
21-AUG-2019 04:36:03.143 1188 [SCX] Unconnected dedicated link requested, creating new parent link (Id = 97)
21-AUG-2019 04:36:03.143 1188 [PL97] Creating dedicated link
21-AUG-2019 04:36:03.143 1188 [PL97] Attaching to socket 0xa38
21-AUG-2019 04:36:03.143 1188 [SVRTHR] 1 AddClient from 127.0.0.1:49812, link is [SCX] 1:15
21-AUG-2019 04:36:03.143 1188 [SCX] 1:15 QP Created
21-AUG-2019 04:36:03.143 052C [SCX] 1:15 InitSecureSession( IN: )
21-AUG-2019 04:36:03.143 052C [SCX] 1:15 Found matching certificate for connection to local IP address 127.0.0.1
21-AUG-2019 04:36:03.143 052C [SCX] 1:15 InitSecureSession( OUT: hr 0 - Ok. )
21-AUG-2019 04:36:03.144 052C [SCX] 1:15 StartSecureSession( IN: )
21-AUG-2019 04:36:03.144 052C [SCX] 1:15 StartSecureSession( OUT: hr 0 - Ok. )
21-AUG-2019 04:36:03.144 0F10 [SCX] 1:15 Entering secure session
21-AUG-2019 04:36:03.144 052C [SCX] 1:15 SetClientDetails( IN: LoggedOn 0, IsLocal 0, User "", Workstation Name "", Client Name "Unknown" )
21-AUG-2019 04:36:03.144 052C [SCX] 1:15 SetClientDetails( OUT: Hr 0 - Ok. )
```

Also attached the file itself.

Cheers!

Attached file: (editor/qs/2moj3739m9y9.log), DB_001 (1).log File size: 839986


Reply From User: JesseChamberlain, posted: 2019-08-22 01:57:48
That does look like the relevant lines. Here's what it looks like when I do it:

22-AUG-2019 00:11:52.355 0374 [SCX] 8:08 QP Created
22-AUG-2019 00:11:52.355 29CC [SCX] 8:08 InitSecureSession( IN: )
22-AUG-2019 00:11:52.356 29CC [SCX] 8:08 Found matching certificate for connection to local IP address 127.0.0.1
22-AUG-2019 00:11:52.356 29CC [SCX] 8:08 InitSecureSession( OUT: hr 0 - Ok. )
22-AUG-2019 00:11:52.356 29CC [SCX] 8:08 StartSecureSession( IN: )
22-AUG-2019 00:11:52.356 29CC [SCX] 8:08 StartSecureSession( OUT: hr 0 - Ok. )
22-AUG-2019 00:11:52.356 0AD8 [SCX] 8:08 Entering secure session
22-AUG-2019 00:11:52.357 29CC [SCX] 8:08 SetClientDetails( IN: LoggedOn 0, IsLocal 0, User "", Workstation Name "", Client Name "Unknown" )
22-AUG-2019 00:11:52.357 29CC [SCX] 8:08 SetClientDetails( OUT: Hr 0 - Ok. )
22-AUG-2019 00:11:52.357 0AD8 [SCX] 8:08 SetClientDetails( IN: Lcid 0xFFFFFFFF, ClientName WTAULVSE0C7BFPL::ScxV6Server )
22-AUG-2019 00:11:52.357 0AD8 [SCX] 8:08 SetClientDetails( OUT: Features 0x8C0F, hr 0 - Ok. )
22-AUG-2019 00:11:52.357 0AD8 [SCX] 8:08 AdviseState( IN: )
22-AUG-2019 00:11:52.357 0AD8 [SCX] 8:08 AdviseState( OUT: hr 0 - Ok. )
22-AUG-2019 00:11:52.360 0AD8 [SCX] 8:08 Advise( IN: Port 5503, ClientId 2 )

So it seems to not be doing the second SetClientDetails for some reason...

If you'd like us to look at it further please raise a support ticket.

See Answer In Context

Share
Reply
Related Products
Schneider Electric
EcoStruxure™ Geo SCADA Expert
Top Experts
User Count
sbeadle
Sisko sbeadle Sisko
188
BevanWeiss
Sisko BevanWeiss
53
AdamWoodland
Lt. Commander AdamWoodland Lt. Commander
16
JChamberlain
Lieutenant JChamberlain Lieutenant
16
AndrewScott
Lieutenant AndrewScott
15
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric