[Imported] Script to amend Historic data with a configurable timestamp
>>Message imported from previous forum - Category:Scripts and Tips<< User: mchartrand, originally posted: 2018-10-19 17:40:39 Id:151 This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum. The original posters' identities have not been included.
-------------------------------
**_For a given point, Is there a script to change the Historic data of a particular timestamp to a new value with any other timestamp ? Ex. For a given Point, changing the 8:10:00 historic value to a new value with 8:30:00 timestamp?_**
-------------------------------
Unfortunately, there's no way to directly do this. You could invalidate the old value or give it a lower qualilty, then add the new value separately.