Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • SCADA & Telemetry Solutions
  • :
  • Geo SCADA Expert Forum
  • :
  • Re: [Imported] Quality Classifications and CurrentQuality
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49530members
Join Now
242876posts
Join Now

[Imported] Quality Classifications and CurrentQuality

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Geo SCADA Expert Forum
Solved
sbeadle
Sisko sbeadle Sisko
Sisko
‎2019-11-06 06:28 AM
0 Likes
1
172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-11-06 06:28 AM

[Imported] Quality Classifications and CurrentQuality

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: brcgomezle, originally posted: 2019-01-08 21:45:43 Id:346
Hi.

I have a system where is common to do maintenance to the sensors we are reading. Each time a maintenance is started, the corresponding points in ClearScada are tagged using Quality Classifications feature, but the CurrentQuality of the point and the quality of the historic value never change from "Good" to "Bad". I'm using this feature such that all maintenances that will generate "bad" qualities won't be considered in my reports (Using historic views).

How can I set a "Bad" quality on my historic values when a Quality Classification is associated to a point?

Thanks for your help.

Solved! Go to Solution.

Labels
  • SCADA
Share
Reply

Accepted Solutions
sbeadle
Sisko sbeadle Sisko
Sisko
‎2019-11-06 06:29 AM
0 Likes
0
171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-11-06 06:29 AM

Re: [Imported] Quality Classifications and CurrentQuality

>>Responses imported from previous forum


Reply From User: sbeadle, posted: 2019-01-09 08:56:45
Approaches I have seen used:
1) Enable 'Put Aside' on the historic tab of all points. Then change your practice to override points in maintenance. This causes storage of data received while overridden into the Put Aside classification, which is not usually displayed on trends or history lists, but can be shown as another trace on trends or queried with slightly different SQL.
2) When the maintenance ends, script code to modify historic data from the start to the end of maintenance period - modified data can have a different quality, such as Bad or Uncertain.
3) Use the historic Validation feature. Validation would then need to be done on all history, because the default state is unvalidated.

 

Reply From User: brcgomezle, posted: 2019-01-09 13:14:31
Your first comment almost leave me hopeless. Cannot believe this feature seems something fancy but useless to its purpose.


I will try your approaches in my local database and then in the real system, I will let you know how it ends. Thanks a lot for your help.


Reply From User: sbeadle, posted: 2019-01-09 13:33:36
Sorry for the first comment - I believe you may be the first to try Quality Classifications! Your feedback is welcome.


Reply From User: brcgomezle, posted: 2019-01-09 13:53:28
Don't worry, is good to know that there are other options anyway. I know how it feels to find a problem that seems nobody knows about.


Reply From User: brcgomezle, posted: 2019-01-10 20:56:42
Hi sbeadle!

I'm trying to script and modify the values stored while the maintenance was performed. I'm using the following function:

oPoint.Interface.Historic.ModifyValue

But this inserts data into the historic values of the point with the quality I set. Do you know the function used in trends called "Modify Range of Values" but through script? I haven't found it.

Thank you


Reply From User: sbeadle, posted: 2019-01-11 09:10:49
ModifyValues is not (yet) available from the API. I believe ModifyValue will change/overwrite the value if the timestamp is exactly the same as the original. This may be a problem in script as vbscript does not support fractional seconds. You could use script to call a Logic program written to read and write values in a range?


Reply From User: brcgomezle, posted: 2019-01-11 15:21:36
I will try it. Once I have the results will let you know.


Reply From User: brcgomezle, posted: 2019-06-26 20:50:34
Hi sbeadle,

I tried with scripts and definitely the best option is to enable Put Aside feature. At the time you need to tag values with 'bad' quality the corresponding point must be overriden. Once the condition is normalized, release the override value.

The put aside values won't appear in a normal CDBHISTORIC query and won't be consider into any HistoricView.

If it is necessary to see the variations while override value is set, at the end of the process Put aside values can be captured from CDBHISTORICALL and inserted into CDBHISTORIC using oPoint.Interface.Historic.InsertValue method with bad quality.

Thanks for your help.

See Answer In Context

Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
1 Reply 1
sbeadle
Sisko sbeadle Sisko
Sisko
‎2019-11-06 06:29 AM
0 Likes
0
172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-11-06 06:29 AM

Re: [Imported] Quality Classifications and CurrentQuality

>>Responses imported from previous forum


Reply From User: sbeadle, posted: 2019-01-09 08:56:45
Approaches I have seen used:
1) Enable 'Put Aside' on the historic tab of all points. Then change your practice to override points in maintenance. This causes storage of data received while overridden into the Put Aside classification, which is not usually displayed on trends or history lists, but can be shown as another trace on trends or queried with slightly different SQL.
2) When the maintenance ends, script code to modify historic data from the start to the end of maintenance period - modified data can have a different quality, such as Bad or Uncertain.
3) Use the historic Validation feature. Validation would then need to be done on all history, because the default state is unvalidated.

 

Reply From User: brcgomezle, posted: 2019-01-09 13:14:31
Your first comment almost leave me hopeless. Cannot believe this feature seems something fancy but useless to its purpose.


I will try your approaches in my local database and then in the real system, I will let you know how it ends. Thanks a lot for your help.


Reply From User: sbeadle, posted: 2019-01-09 13:33:36
Sorry for the first comment - I believe you may be the first to try Quality Classifications! Your feedback is welcome.


Reply From User: brcgomezle, posted: 2019-01-09 13:53:28
Don't worry, is good to know that there are other options anyway. I know how it feels to find a problem that seems nobody knows about.


Reply From User: brcgomezle, posted: 2019-01-10 20:56:42
Hi sbeadle!

I'm trying to script and modify the values stored while the maintenance was performed. I'm using the following function:

oPoint.Interface.Historic.ModifyValue

But this inserts data into the historic values of the point with the quality I set. Do you know the function used in trends called "Modify Range of Values" but through script? I haven't found it.

Thank you


Reply From User: sbeadle, posted: 2019-01-11 09:10:49
ModifyValues is not (yet) available from the API. I believe ModifyValue will change/overwrite the value if the timestamp is exactly the same as the original. This may be a problem in script as vbscript does not support fractional seconds. You could use script to call a Logic program written to read and write values in a range?


Reply From User: brcgomezle, posted: 2019-01-11 15:21:36
I will try it. Once I have the results will let you know.


Reply From User: brcgomezle, posted: 2019-06-26 20:50:34
Hi sbeadle,

I tried with scripts and definitely the best option is to enable Put Aside feature. At the time you need to tag values with 'bad' quality the corresponding point must be overriden. Once the condition is normalized, release the override value.

The put aside values won't appear in a normal CDBHISTORIC query and won't be consider into any HistoricView.

If it is necessary to see the variations while override value is set, at the end of the process Put aside values can be captured from CDBHISTORICALL and inserted into CDBHISTORIC using oPoint.Interface.Historic.InsertValue method with bad quality.

Thanks for your help.

See Answer In Context

Share
Reply
Top Experts
User Count
BevanWeiss
Admiral BevanWeiss
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric