I recently had to answer some questions about Put Aside, so here is a summary just in case anyone here is interested!
When you override a point value in the master, the current value of the point is fixed to the overridden value. But receipt of data carries on 'internally'. 'Put Aside' is the name given to this data which is (almost) ignored during the override.
a) With no special configuration, ClearSCADA will save values gathered while a point has a Master Override – and store them in the point columns PutAsideValueFormatted, PutAsideTime ' etc
b) Also, when you override and then release, the historic list and trend will show:
. 1. Override to the selected value
. 2. Release at the same selected value
. 3. Another historic value at the same time as the release, for the value last received from the point through its protocol (the most recent put aside value, if there is one, or the original value before the override, if there isn't)
c) When you configure a point and enable historic put aside on the point form, the master will save additional historic values received from site during the override.
d) These are not visible in the menu ‘Display Historic List' or ‘Display Historic Trend'
e) To add them to a trend, drag on/create a trace and select ‘Raw Historic'. Click the trace settings ‘Advanced' button and select ‘Extended Source Filter' and ‘Put Aside'. This trace only shows put aside data.
f) To add them to a list, click Edit Query on the normal Historic List, and:
. 1. Add the column PutAside, which is true for this type of data
. 2. Change the table from ‘CDBHistoric' to ‘CDBHistoricAll'
Hope this helps!! See the attached picture.
[]((see attachments below) nz/x6gyge0a6y2d.png "")
Attached file: (editor/nz/x6gyge0a6y2d.png), put aside.PNG File size: 215936
Solved! Go to Solution.
>>Responses imported from previous forum
Reply From User: BevanWeiss, posted: 2019-07-19 09:13:36
I think there is a Server Config item which modifies some of this behaviour also (just to make it a little more confusing )
Reply From User: sbeadle, posted: 2019-07-19 10:05:04
Thanks [at]BevanWeiss I'm not aware/can't find one?
Reply From User: BevanWeiss, posted: 2019-08-06 04:10:07
[at]sbeadle said:
Thanks [at]BevanWeiss I'm not aware/can't find one?
I've had a look, and I think I'm wrong... I can't find the setting that I was thinking of. So it was obviously all just a dream... never mind me.
>>Responses imported from previous forum
Reply From User: BevanWeiss, posted: 2019-07-19 09:13:36
I think there is a Server Config item which modifies some of this behaviour also (just to make it a little more confusing )
Reply From User: sbeadle, posted: 2019-07-19 10:05:04
Thanks [at]BevanWeiss I'm not aware/can't find one?
Reply From User: BevanWeiss, posted: 2019-08-06 04:10:07
[at]sbeadle said:
Thanks [at]BevanWeiss I'm not aware/can't find one?
I've had a look, and I think I'm wrong... I can't find the setting that I was thinking of. So it was obviously all just a dream... never mind me.