>>Message imported from previous forum - Category:ClearSCADA Software<<
User: jdietz, originally posted: 2019-02-12 23:14:40 Id:367
Hi Everyone,
We're working on transitioning our installed system from FlowStation 110's to SP334's. During our initial setup, the FS110s were configured as MODBUS devices, and register assignments followed that seamlessly.
Now we're setting things up as DNP3, and finding questions faster than answers. As we were working on adding DNP points to the DB, we tried to configure a point with a bit offset to utilize a 16-bit register for multiple digital points. This is something we do regularly with MODBUS. However, when configuring DNP points in CS we found that options for bit offset are non-existent, as is the ability to type a colon or slash after the register to define a certain starting bit.
My question is for anyone who is knowledgeable with DNP3:
Does DNP allow for bit offset, and if so, how do you configure it in CS when working on your point?
>>Responses imported from previous forum
Reply From User: dmercer, posted: 2019-02-13 03:30:47
That's not something that you can do in DNP3. Digital and analog values are completely separate.
You could manually unpack the binary points from an analog value at the receiver end, but it would be better to remap your points so that binary points are sent as individual DNP3 binary points. This will let you use unsolicited responses properly, which is (IMO) the main benefit of DNP3.
Reply From User: jdietz, posted: 2019-02-13 17:21:45
That's what I was afraid of, but also expecting. It's not a huge issue, since we just need to modify our DNP table.
Thank you for helping to clear some of the fog around this for me!
>>Responses imported from previous forum
Reply From User: dmercer, posted: 2019-02-13 03:30:47
That's not something that you can do in DNP3. Digital and analog values are completely separate.
You could manually unpack the binary points from an analog value at the receiver end, but it would be better to remap your points so that binary points are sent as individual DNP3 binary points. This will let you use unsolicited responses properly, which is (IMO) the main benefit of DNP3.
Reply From User: jdietz, posted: 2019-02-13 17:21:45
That's what I was afraid of, but also expecting. It's not a huge issue, since we just need to modify our DNP table.
Thank you for helping to clear some of the fog around this for me!
Discuss challenges in energy and automation with 30,000+ experts and peers.
Find answers in 10,000+ support articles to help solve your product and business challenges.
Find peer based solutions to your questions. Provide answers for fellow community members!