>>Message imported from previous forum - Category:ClearSCADA Software<<
User: Craig_Scott, originally posted: 2019-08-19 05:59:36 Id:486
Has anyone seen ClearSCADA operating in an MV based application (protection relays / MV switchgear) using IEC61850 protocol? Any 3rd party drivers you know of that is suitable?

1 REPLY 1
Admiral

Re: [Imported] ClearSCADA Protocol Support IEC61850

>>Responses imported from previous forum


Reply From User: geoffpatton, posted: 2019-08-19 13:59:23
I usually turn to kepware when ClearSCADA does not have a driver.They have a 61850 driver, i have not used it though.
I setup a substation that has 61580 the relays were using it to pass information to each other, but we used DNP3 for the SCADA. 61850 is only supposed to be used inside the substation.


Reply From User: Craig_Scott, posted: 2019-08-19 23:26:52
Thanks for the advice Geoff


Reply From User: geoffpatton, posted: 2019-08-20 16:56:48
You are welcome hope all goes well.