Hi,

I wish to have clarification.

 

We have to connect GeoSCADA to a Web Gateway that will be communicating via SOAPui with XML / Json files.

 

From what I have read GeoSCADA has no means to de-serialise this format internally?

 

If this is the case, a Web Server / Client is to built in order to de-serialise the XML files and write values to internal GeoSCADA points via OPC? 

(a driver to be created by the DDK).

 

An additional Web Server / Client cannot be avoided to achieve this path of communications.

 

Thanks,

 

 

2 REPLIES 2
Highlighted
Commander

Re: GeoSCADA Web Service Capability

Correct, you will need to develop an intermediate 'application' which is able to act as a client to both your 'Web Gateway', and also to Geo SCADA Expert / ClearSCADA (whether via SOAP / .NET API / Automation Interface / Simple DDK).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Highlighted
Commander

Re: GeoSCADA Web Service Capability

I believe that my answer has addressed the question that you asked.  Please mark it as the solution.


Lead Control Systems Engineer for Alliance Automation (VIC).