Sign In Help
Schneider Electric
HelpLogin / Register

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Communities
  • :
  • SCADA & Telemetry Solutions
  • :
  • Geo SCADA Expert Forum
  • :
  • Re: GeoSCADA 6.80.7641.1 License shows DNP3 enabled, Server Status shows DNP3 status = no license
Community Menu
  • Forums
    • By Topic
        • EcoStruxure Building
          • Field Devices Forum
        • EcoStruxure Power & Grid
          • Metering & Power Quality
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Automation Forum
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
          • Motorabgangstechnik & Antriebstechnik Forum
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Solutions for Motor Management
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
          • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
        • Power Distribution NEMA
          • US Utility Forum
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure Building
        • Field Devices Forum
      • EcoStruxure Power & Grid
        • Metering & Power Quality
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Automation Forum
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
        • Motorabgangstechnik & Antriebstechnik Forum
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Solutions for Motor Management
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
        • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Power Distribution NEMA
        • US Utility Forum
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • EcoStruxure Power & Grid
          • Backstage Access Resources
        • Industrial Automation
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
          • UK&I Residential and Commercial Electrical Distribution
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
          • Solutions for eMobility
          • Digital Hospital Solutions – UK&I
        • Knowledge Center
          • Industrial Automation How-to videos
          • Digital E-books
          • Success Stories Corner
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
        • Retail
          • Solutions for eMobility
        • Retail
          • Digital Hospital Solutions – UK&I
      • EcoStruxure Power & Grid
        • Backstage Access Resources
      • Industrial Automation
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
        • UK&I Residential and Commercial Electrical Distribution
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
        • Solutions for eMobility
        • Digital Hospital Solutions – UK&I
      • Knowledge Center
        • Industrial Automation How-to videos
        • Digital E-books
        • Success Stories Corner
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
      • Retail
        • Solutions for eMobility
      • Retail
        • Digital Hospital Solutions – UK&I
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Register Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
53117members
248546posts

GeoSCADA 6.80.7641.1 License shows DNP3 enabled, Server Status shows DNP3 status = no license

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Geo SCADA Expert Forum
Solved
Critcho
Crewman Critcho
Crewman
‎2021-02-24 09:27 AM
0 Likes
8
395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-24 09:27 AM

GeoSCADA 6.80.7641.1 License shows DNP3 enabled, Server Status shows DNP3 status = no license

Hi guys,

 

I've set up a test server, using a licence dongle. I tried to set up a DNP3 TCP direct channel, but it was always failed; Quality = Device Failure. When I tried to enable logging on the comms channel per https://tprojects.schneider-electric.com/GeoSCADAHelp/Geo%20SCADA%202020/Default.htm#ServerAdministr..., I noticed that it shows DNP3 as "No License". But my License Details shows DNP3 is enabled. What am I missing here?

 

2021-02-23 GeoSCADA Licence shows DNP enabled but Serve Status shows DNP not licensed - Censored.png

Thanks for your help,

Scott

Labels
  • DNP3
  • SCADA
  • WITS
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply

Accepted Solutions
AdamWoodland
Commander AdamWoodland Commander
Commander
‎2021-02-24 12:38 PM
1 Like
7
390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-24 12:38 PM

Re: GeoSCADA 6.80.7641.1 License shows DNP3 enabled, Server Status shows DNP3 status = no license

That's usually caused by having unlicensed extensions to the DNP3 driver, if you have them installed and one isn't licensed it takes the whole driver out. Run the installer and check, given you have the core DNP3 and DNP3 WITS you probably have the ENET extension installed but not licensed.

See Answer In Context

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
8 Replies 8
AdamWoodland
Commander AdamWoodland Commander
Commander
‎2021-02-24 12:38 PM
1 Like
7
391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-24 12:38 PM

Re: GeoSCADA 6.80.7641.1 License shows DNP3 enabled, Server Status shows DNP3 status = no license

That's usually caused by having unlicensed extensions to the DNP3 driver, if you have them installed and one isn't licensed it takes the whole driver out. Run the installer and check, given you have the core DNP3 and DNP3 WITS you probably have the ENET extension installed but not licensed.

See Answer In Context

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
BevanWeiss
Sisko BevanWeiss
Sisko
‎2021-02-24 02:48 PM
0 Likes
5
385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-24 02:48 PM

Re: GeoSCADA 6.80.7641.1 License shows DNP3 enabled, Server Status shows DNP3 status = no license

As Adam said, WITS, ENET and x70 are potential extensions which aren't the generic DNP3 licence (although ENET and x70 are out of the box licences... I'm think WITS may be an extra costed licence)


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
AdamWoodland
Commander AdamWoodland Commander
Commander
‎2021-02-24 03:07 PM
0 Likes
4
382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-24 03:07 PM

Re: GeoSCADA 6.80.7641.1 License shows DNP3 enabled, Server Status shows DNP3 status = no license

What's odd is the screenshot of the licence isn't showing the standard out of the box licence with all the standard drivers included. So wondering if this was something special someone was testing.

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
BevanWeiss
Sisko BevanWeiss
Sisko
‎2021-02-24 06:54 PM
0 Likes
3
369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-24 06:54 PM

Re: GeoSCADA 6.80.7641.1 License shows DNP3 enabled, Server Status shows DNP3 status = no license

Ohh right yeah... that dongle licence looks super dodgy.

 

Either it was generated really badly outside of Schneider, or it was very badly generated internally within Schneider.

In the first case, I'd suggest joining a witness protection program and not speaking of this again... in the second case I'd raise it with your Schneider support contact, and get the dongle code re-generated.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
geoffpatton
Lt. Commander geoffpatton
Lt. Commander
‎2021-02-25 06:21 AM
0 Likes
0
347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-25 06:21 AM

Re: GeoSCADA 6.80.7641.1 License shows DNP3 enabled, Server Status shows DNP3 status = no license

It could be some specially negotiated low cost minimum licensing.

 

At my previous company we did this with Citect. the licensing would only run as a single server, with Modbus and like 1500 points.

It was supposed to be a easier foot in the door and then get them to upgrade. It was kind of a flop. I only recall a few installations, and they did not grow. very small municipalities.

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
Critcho
Crewman Critcho
Crewman
‎2021-02-25 10:44 AM
0 Likes
0
330
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-25 10:44 AM

Re: GeoSCADA 6.80.7641.1 License shows DNP3 enabled, Server Status shows DNP3 status = no license

Thanks @AdamWoodland, looks like that was the issue. I uninstalled DNP3.SCADAPack E (Kept DNP3.WITS), still didn't work. I then went through the installer again, and uninstalled anything that I absolutely didn't need; I'm guessing Schneider Electric SCADAPack x70.DNP3 Protocol was the problem. This must have been installed by default, I have absolutely no need for it, I wouldn't have picked it manually.

 

I know GeoSCADA is a massive system, and this problem is rare, but it could have been handled better, instead of leaving me guessing.

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
Critcho
Crewman Critcho
Crewman
‎2021-02-25 10:44 AM
0 Likes
1
329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-25 10:44 AM

Re: GeoSCADA 6.80.7641.1 License shows DNP3 enabled, Server Status shows DNP3 status = no license

@BevanWeiss there is nothing "dodgy" about the licence, and I'm surprised to see remarks like that on what I thought was a professional forum. It is a cut-down licence specifically generated for suppliers to test their equipment against GeoSCADA using the WITS protocol.

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
BevanWeiss
Sisko BevanWeiss
Sisko
‎2021-02-25 02:06 PM
0 Likes
0
319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-25 02:06 PM

Re: GeoSCADA 6.80.7641.1 License shows DNP3 enabled, Server Status shows DNP3 status = no license

@Critcho 

dodgy
adjective

 UK informal

  - likely to fail or cause problems

 

Given you were posting to a forum about how the licence is causing you problems, tell me again how this was not dodgy?

 

I would have expected that with such a cut down licence, which is most definitely not 'normal', there would have been some specific use-instructions associated with it.  So when installing a ClearSCADA / Geo SCADA Expert installation you would have had details on exactly which boxes in the installer to tick for this particular licence.

 

All that aside, you get what you pay for.. both in licences, and in forums 😉


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
Top Experts
User Count
sbeadle
Sisko sbeadle Sisko
188
BevanWeiss
Sisko BevanWeiss
56
AndrewScott
Lt. Commander AndrewScott
18
AdamWoodland
Commander AdamWoodland Commander
17
JChamberlain
Lt. Commander JChamberlain Lt. Commander
16
geoffpatton
Lt. Commander geoffpatton
10
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2021, Schneider Electric