Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • SCADA & Telemetry Solutions
  • :
  • Geo SCADA Expert Forum
  • :
  • Re: Geo SCADA VB capability
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
50948members
Join Now
244959posts
Join Now

Geo SCADA VB capability

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Geo SCADA Expert Forum
Solved
DavidSkilbeck
Lieutenant DavidSkilbeck
Lieutenant
‎2020-09-03 04:31 PM
0 Likes
4
477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-03 04:31 PM

Geo SCADA VB capability

Hi, 

I have a couple of questions regarding Geo SCADA VB capabilities.

 

Is it possible

 

* to do a binary file read. Example below in Python, but something like

 

# Get Data out of Binary File
def readdata(filename,i):
'''Read data from a file. Data count is in the header'''
with open(filename, "rb") as file:
buffer = file.read(20)
size, variation, objectType, pointIndex, startTime, sampleRate, count = struct.unpack('>IBBHIII', buffer)
print(size, variation, objectType, startTime, sampleRate, count)

 

 

* to calculate Epoch time. Again example below in Python, but something like

 

startTime = time.strftime('%Y-%m-%d %H:%M:%S', time.localtime(struct.unpack('>i', byte)[0]))

 

 

are there builtin functions for these.

Thanks,

Solved! Go to Solution.

Labels
  • SCADA
Tags (1)
  • Tags:
  • english
Share
Reply

Accepted Solutions
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-09-03 10:30 PM
0 Likes
3
464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-03 10:30 PM

Re: Geo SCADA VB capability

If we are talking about Geo SCADA ViewX Client-side VBscript then 'yes', it's possible.

But no, it's not a GeoSCADA 'builtin function'

 

With VBscript you are able to call pretty much any COM type of object.

 

Like thus...

https://stackoverflow.com/questions/6060529/read-and-write-binary-file-in-vbscript

 

 

And to calculate epoch time (yucky)

https://gist.github.com/sean-m/12e225436215c3358afb

 

But epoch is just a fixed time reference, so if you just use NOW and then subtract the fixed time (of epoch) then you would have the 'time since epoch'.  You should not need to actually calculate epoch (since it is by definition in the Unix world 01/01/1970 00:00:00+00:00).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
4 Replies 4
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-09-03 10:30 PM
0 Likes
3
465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-03 10:30 PM

Re: Geo SCADA VB capability

If we are talking about Geo SCADA ViewX Client-side VBscript then 'yes', it's possible.

But no, it's not a GeoSCADA 'builtin function'

 

With VBscript you are able to call pretty much any COM type of object.

 

Like thus...

https://stackoverflow.com/questions/6060529/read-and-write-binary-file-in-vbscript

 

 

And to calculate epoch time (yucky)

https://gist.github.com/sean-m/12e225436215c3358afb

 

But epoch is just a fixed time reference, so if you just use NOW and then subtract the fixed time (of epoch) then you would have the 'time since epoch'.  You should not need to actually calculate epoch (since it is by definition in the Unix world 01/01/1970 00:00:00+00:00).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
DegMet
Crewman DegMet
Crewman
‎2021-01-12 07:26 AM
0 Likes
2
220
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-01-12 07:26 AM

Re: Geo SCADA VB capability

Hi @BevanWeiss,

 

I have a need related with Unix Time conversion. We are migrating an OASyS DNA SCADA to a GeoSCADA system. I've found a variable that represent a timestamp (from a remote event logger system), and I assume the format as Unix time, because the tag name (Unix_TS) and the following script:

 

Public Sub rt_TimeStamp_ValueChanged(ByVal sender As System.Object, ByVal e As System.EventArgs) Handles rt_TimeStamp.ValueChanged
Try
' Insert user code here.
Dim DT As DateTime = New DateTime(1970, 1, 1, 0, 0, 0)

dt = DT.AddSeconds(CDbl( rt_TimeStamp.Text ))
rt_timestamp_text.Text = dt.ToString("dd/MM/yyyy HH:mm:ss")
' End user code here.
Catch ex As Exception
DNALog.WriteLog(DNALog.LogLevel.Always, "Event handler rt_TimeStamp.ValueChanged on display " + Model.InstanceName + " failed: " + ex.Message)
End Try
End Sub

 

I have to implement this conversion in GeoScada, I mean given a Unix time to convert it in a human readable form.

Is there a direct funtion to do that? or should I implement some ST code or may be some script?

 

I've trying to convert this code (https://www.geeksforgeeks.org/convert-unix-timestamp-to-dd-mm-yyyy-hhmmss-format/) to ST script, but there's no break tag inside a while loop in GeoScada :(.

 

Thanks

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2021-01-12 08:44 PM
1 Like
0
207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-01-12 08:44 PM

Re: Geo SCADA VB capability

@DegMet 

New question... new topic.  Please don't try to thread hijack.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
sbeadle
Sisko sbeadle Sisko
Sisko
‎2021-01-19 02:08 AM
0 Likes
0
157
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-01-19 02:08 AM

Re: Geo SCADA VB capability

Hi. Yes, please raise as another thread because it's a new subject.

(There are Logic functions to get an absolute time and offset by a number of seconds or milliseconds).

Tags (6)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Share
Reply
Top Experts
User Count
sbeadle
Sisko sbeadle Sisko
188
BevanWeiss
Admiral BevanWeiss
51
AdamWoodland
Lt. Commander AdamWoodland Lt. Commander
16
JChamberlain
Lieutenant JChamberlain Lieutenant
16
AndrewScott
Lieutenant AndrewScott
14
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric