Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • SCADA & Telemetry Solutions
  • :
  • Geo SCADA Expert Forum
  • :
  • Geo SCADA Dual Tag Possibilities
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49224members
Join Now
242436posts
Join Now

Geo SCADA Dual Tag Possibilities

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to Geo SCADA Expert Forum
DavidSkilbeck
Lieutenant DavidSkilbeck
Lieutenant
‎2020-01-16 04:01 PM
0 Likes
7
1191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-16 04:01 PM

Geo SCADA Dual Tag Possibilities

Hi,

is it possible in Geo SCADA for points to be referenced by two names.

 

The reason for the question is;

 

It would be good to continue to use existing point reference names in order to maintain existing systems connections (i.e. eDNA etc).

 

To be able to create new reference names that adhere to an overall standard point naming convention.

 

 

Thanks,

Labels
  • SCADA
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
7 Replies 7
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-01-16 04:12 PM
0 Likes
0
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-16 04:12 PM

Re: Geo SCADA Dual Tag Possibilities

What do you mean by 'tags'?  There is no such terminology within ClearSCADA / Geo SCADA Expert.

 

If you mean, is it possible to have two Points (i.e. derived from CDBPoint) which have the same combined Scanner/Outstation and Address?  Then the answer is: it depends on the driver.

Most drivers do not allow this.  They optimise their polling based upon 'an address' only appearing once within their per-outstation tables.

 

There are some drivers, like the OPC Driver(s) which do allow duplicate addresses.

I'm not sure whether there is any documented detail of which do and which don't unfortunately.

 

But I would consider the general rule as, 'no' this is not allowed (with some drivers being the exception).

 

ClearSCADA / Geo SCADA Expert internally uses OID references, so renaming / moving points is generally straight forward and all changes are handled automatically by the ClearSCADA / Geo SCADA Expert subsystems.  Hadcoded FullName references (i.e. in SQL queries etc) are NOT updated automatically of course.. and these would need to be done manually.

 

There are kind of some ways to get around it.  You could create a Calculation Point where the 'old' Point existed, and just have it point towards the 'new' Point.  It could then be configured to get the same value as the field point.  I would not recommend it however.

I would recommend changing where eDNA is pointing for its source data so that it matches the new standardised naming.  Depending on how eDNA is retrieving its data from ClearSCADA / Geo SCADA Expert this might or might not result in some data loss.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
AdamWoodland
Lt. Commander AdamWoodland Lt. Commander
Lt. Commander
‎2020-01-16 05:36 PM
0 Likes
2
1179
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-16 05:36 PM

Re: Geo SCADA Dual Tag Possibilities

Two possible options spring to mind:

 

1. If using OPC, check out search keys with the tag option enabled. They provide an alternative reference for objects. Search keys are a special kinda of metadata field, and if you need some more generic way of addressing objects the standard metadata fields could be used

 

2. If only for alarming (i.e. for showing on the alarm banner), check out the Alarm Source field under the Alarm tab

Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-01-26 11:28 PM
0 Likes
1
1121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-26 11:28 PM

Re: Geo SCADA Dual Tag Possibilities

Do the Search Keys also work for OPC-HDA?

I've had a few systems with OSIsoft PI using the OPC-HDA interface.  When we've moved around points things have gotten broken, I could see some uses for the Search Key stuff to keep things somewhat 'fixed'.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
AdamWoodland
Lt. Commander AdamWoodland Lt. Commander
Lt. Commander
‎2020-01-27 03:16 PM
0 Likes
0
1113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-27 03:16 PM

Re: Geo SCADA Dual Tag Possibilities

Should do, it is all just OPC, although I've never tried it with OPC-HDA... although last time I used it for OPC-DA was 15-odd years ago so could have changed since.

Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-01-30 11:54 PM
0 Likes
2
1080
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-30 11:54 PM

Re: Geo SCADA Dual Tag Possibilities

@DavidSkilbeck I don't think you're going to get a better answer than Adam's OPC Search Key.  You should mark that as the answer I think.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
DavidSkilbeck
Lieutenant DavidSkilbeck
Lieutenant
‎2020-02-16 04:55 PM
0 Likes
1
1005
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-16 04:55 PM

Re: Geo SCADA Dual Tag Possibilities

Hi,

I take it we are on the right track? Thanks,

 

SecondaryPointName.PNG

Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-02-16 05:07 PM
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-16 05:07 PM

Re: Geo SCADA Dual Tag Possibilities

Unsure.. that screenshot is not in the slightest bit helpful 😉

 

Maybe try a screenshot that shows what you have configured the Metadata field as.

 @AdamWoodland is the man that has had this working before, I've never tried it... but the help suggests that the 'Tag' tick box is the essential item here... the other thing that will be important will be the Size.. obviously if you don't make this long enough to hold your search string, then things will work badly

2020-02-17 12_04_30-VM_WS2019 ClearSCADA 2015R2 - VMware Workstation.png

 

Here's the help reference (for US English apparently..)

file:///C:/ProgramData/Schneider%20Electric/ClearSCADA/Help_en-US/Content/ServerAdministrationGuide/DefinewhetheraSearchKeyFieldcanalsobeusedasanOPCTag.htm#

 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
Top Experts
User Count
BevanWeiss
Admiral BevanWeiss
2
sbeadle
Sisko sbeadle Sisko
1
geoffpatton
Lieutenant geoffpatton
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric