  • Geo SCADA Bulk Location Configuration
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51132members
Join Now
245261posts
Join Now

Geo SCADA Bulk Location Configuration

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Geo SCADA Expert Forum
Solved
Cbhasin
Ensign Cbhasin
Ensign
‎2020-03-03 07:22 PM
0 Likes
14
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-03 07:22 PM

Geo SCADA Bulk Location Configuration

Is there a way to bulk configure the location property of points to "Static" (About a thousand points). I tried using the Bulk Editor, but it can only be a boolean. I tried setting it to True, but it didn't help either. Maybe there is an Aggregate I should look into and write a script? What would be the recommended way?

Thank you!

Solved! Go to Solution.

Labels
  • SCADA
  • Scripting
  • ViewX
Tags (3)
  • Tags:
  • aggregate
  • location
  • OPC Property
Share
Reply

Accepted Solutions
sbeadle
Sisko sbeadle Sisko
Sisko
‎2020-03-05 01:23 AM
0 Likes
0
1827
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-05 01:23 AM

Re: Geo SCADA Bulk Location Configuration

Hi @BevanWeiss . Yes, I think so. At the time it was created I am not sure that aggregates with multiple child choices existed or were commonly needed to be edited, so the Bulk Editor did not need to support it. This should be asked of the support team.

Thanks.

Steve

See Answer In Context

Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
14 Replies 14
Hardin4019
Lieutenant Hardin4019
Lieutenant
‎2020-03-04 05:49 AM
0 Likes
3
1873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-04 05:49 AM

Re: Geo SCADA Bulk Location Configuration

To the best of my knowledge the location of a point is "Inherited" from the Parent Group, and if that parent Group has its location "Inherited" it could come from as far up the DB Tree as the Root. So I would think the easy way is to make sure that all of the points and groups have the location set to inherited down to a specific group containing your ~1000 points, then change that group to "Static" and enter the new location information. Then all of the points within that group should be good.

Share
Reply
geoffpatton
Lt. Commander geoffpatton
Lt. Commander
‎2020-03-04 06:02 AM
0 Likes
3
1872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-04 06:02 AM

Re: Geo SCADA Bulk Location Configuration

Looks like it is a bug in the Bulk Edit tool. You should report it to your local Schneider support team.

 

Since the Bulk Edit does not work I would change it using SQL the value to update that property to, will be a 1.

 

There are 4 options to set for the source and their numeric values are 0-3, Static is the second one so it is 1.

 

Share
Reply
Cbhasin
Ensign Cbhasin
Ensign
‎2020-03-04 04:36 PM
0 Likes
2
1856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-04 04:36 PM

Re: Geo SCADA Bulk Location Configuration

@Hardin4019  Changing the Location Config of the group didn't change that of the points under it.

 

Share
Reply
Cbhasin
Ensign Cbhasin
Ensign
‎2020-03-04 04:52 PM
0 Likes
2
1854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-04 04:52 PM

Re: Geo SCADA Bulk Location Configuration

SQL is giving me the same error: "expects type Boolean, but 1 is Integer" 

Share
Reply
BevanWeiss
Sisko BevanWeiss
Sisko
‎2020-03-04 04:57 PM
1 Like
1
1853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-04 04:57 PM

Re: Geo SCADA Bulk Location Configuration

Nor should it 🙂

 

If the child items are set to 'Inherited' for the GeoLocationSource property then they will have the GeoLocationLatitude and GeoLocationLongitude of their parent group.

 

Depending on how you intend on using the Geo Location configuration will determine if this works for you or doesn't.

 

My recommendation is to have the GeoLocationSource defined as 'Static' or 'Dynamic' as high up the tree as makes sense for your application.  I would normally NOT consider this to be at a point level.  Since points would normally be associated with a group which represents a device, or a group of such devices which represent a site.

I don't see significant benefit in having GeoLocation tagged for 'Fault', when it could instead be tagged for 'Pump 1', or for 'SPS234 - Martin Ave'.

 

When you do a query, the GeoLocationSource = 'True' appears to be for anything except for 'Inherited' / 'None'.

Which is normally ideal, as long as you have it only set to 'Static' / 'Dynamic' at sensible locations.

 

Having a dozen stacked map symbols for Running, Fault, Manual, Auto, Current, No Flow, Duty all because you have set each of these pump point as 'Static' is bad... mmmkkaaayy...

Having a single item which represents the Pump location 'may' be better... (I would perhaps do this in a lagoon system, or a large treatment plant).. for sites like SPSs where the pumps and well are naturally so close together, then I would ONLY have 'Static' set at the site group, and all items beneath it will 'Inherit' this location.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
BevanWeiss
Sisko BevanWeiss
Sisko
‎2020-03-04 04:58 PM
0 Likes
1
1852
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-04 04:58 PM

Re: Geo SCADA Bulk Location Configuration

Can you include your full SQL query?


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
Cbhasin
Ensign Cbhasin
Ensign
‎2020-03-04 05:08 PM
0 Likes
0
1847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-04 05:08 PM

Re: Geo SCADA Bulk Location Configuration

I agree. I think I should have explained it better. I need to set the Location for 1000 different sites (not points, I was just using points as a proof of concept for now). I need to change the GeoLocationSource Property to Static for all of them. Would you please be able to recommend a way to do that?

Cheers

Share
Reply
Cbhasin
Ensign Cbhasin
Ensign
‎2020-03-04 07:21 PM
0 Likes
5
1841
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-04 07:21 PM

Re: Geo SCADA Bulk Location Configuration

@BevanWeiss  @geoffpatton  @Hardin4019 I was able to Set the Location Source to Static using the Automation Interface (VB):

I am assuming that I had written the query wrong.

 

Obj = Svr.FindObject("Example Projects.New Analog Point")
Aggr = Obj.Aggregate("GISLocationSource")
Aggr.Enable = True

 

Thank you!

Share
Reply
BevanWeiss
Sisko BevanWeiss
Sisko
‎2020-03-04 07:24 PM
0 Likes
4
1837
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-04 07:24 PM

Re: Geo SCADA Bulk Location Configuration

On the SQL front, I don't believe you had.

I think this may indeed be a bug, although it's been a while since I played around with SQL and aggregates also, so perhaps I'm also doing it wrong.

 

It would be worth you reporting it to Tech Support.  There's potentially two situations:

a) We're all doing the query wrong, in which case great.  It's just the documentation situation that needs to be improved.

b) There is a valid bug. In which case the bug should be fixed, and the documentation situation should be improved.

 

 

Regards,


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
Cbhasin
Ensign Cbhasin
Ensign
‎2020-03-04 07:24 PM
0 Likes
0
1836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-04 07:24 PM

Re: Geo SCADA Bulk Location Configuration

Update CDBObject SET GISLocationSource = 1 WHERE Id =(SELECT Id FROM CDBObject WHERE FullName LIKE 'Example Projects.Internal.Bla.Bla point)


*** Prepare failed - Query error. ***
*** Column GISLOCATIONSOURCE expects type Boolean, but 1 is Integer.

Cannot write to column 'GISLocationSource'. ***

Share
Reply
Cbhasin
Ensign Cbhasin
Ensign
‎2020-03-04 07:26 PM
0 Likes
3
1835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-04 07:26 PM

Re: Geo SCADA Bulk Location Configuration

Will let Support know. 🙂

Share
Reply
sbeadle
Sisko sbeadle Sisko
Sisko
‎2020-03-05 01:13 AM
1 Like
2
1831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-05 01:13 AM

Re: Geo SCADA Bulk Location Configuration

The answer is:

c) There is no interface to create aggregates or switch between them from SQL. You may request this feature through support.

 

Share
Reply
BevanWeiss
Sisko BevanWeiss
Sisko
‎2020-03-05 01:17 AM
0 Likes
1
1829
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-05 01:17 AM

Re: Geo SCADA Bulk Location Configuration

@sbeadle Is it expected that the Bulk Edit Tool should have been capable of this kind of functionality?

 

Maybe it's a double request situation.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
sbeadle
Sisko sbeadle Sisko
Sisko
‎2020-03-05 01:23 AM
0 Likes
0
1828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-05 01:23 AM

Re: Geo SCADA Bulk Location Configuration

Hi @BevanWeiss . Yes, I think so. At the time it was created I am not sure that aggregates with multiple child choices existed or were commonly needed to be edited, so the Bulk Editor did not need to support it. This should be asked of the support team.

Thanks.

Steve

See Answer In Context

Share
Reply
Related Products
Schneider Electric
EcoStruxure™ Geo SCADA Expert
Top Experts
User Count
sbeadle
Sisko sbeadle Sisko
188
BevanWeiss
Sisko BevanWeiss
52
AdamWoodland
Lt. Commander AdamWoodland Lt. Commander
16
JChamberlain
Lieutenant JChamberlain Lieutenant
16
AndrewScott
Lieutenant AndrewScott
15
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric