Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • SCADA & Telemetry Solutions
  • :
  • Geo SCADA Expert Forum
  • :
  • Geo Map object left mouse click
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49248members
Join Now
242460posts
Join Now

Geo Map object left mouse click

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Geo SCADA Expert Forum
Solved
Johnny07
Crewman Johnny07
Crewman
‎2019-12-24 01:43 AM
0 Likes
8
1555
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-12-24 01:43 AM

Geo Map object left mouse click

Hello, we made a query to display objects on a map based on gps location.

we are able to right click on the object to show a menu, like below

menu.JPG

 

we would like to disable the right click options and instead to navigate with a left click to a mimic relative to the object displayed (an instance in this case).

 

is this possible? if yes how?

 

Thanks in advance,

 

Johnny Bos

 

 

Solved! Go to Solution.

Labels
  • Mimics
  • SCADA
  • ViewX
Share
Reply

Accepted Solutions
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-01-03 01:56 AM
0 Likes
3
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-03 01:56 AM

Re: Geo Map object left mouse click

Hi @Jimi 

Unless GeoSCADA Expert has changed in the past few weeks, the Map displays are not standard Mimics. They don't really have layers that can be freely configured with mimic objects etc.

It's just an embedded webkit engine which has a javascript WMS engine streamed into it, and some hooks into the ClearSCADA query engine.

 

There are ways to get data into the map displays, via customised User Queries which can return HTML that the webkit engine can then follow.  But to do such it would first need to pull up the POI popup, which would require browsing over a POI.. then it would need a click within the POI popup.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
8 Replies 8
Jimi
Lt. Commander Jimi Lt. Commander
Lt. Commander
‎2020-01-03 01:40 AM
0 Likes
7
1515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-03 01:40 AM

Re: Geo Map object left mouse click

on the map layer you could create an invisible box & have a hyperlink method configured on it (ie. to a faceplate mimic). Once the user clicks it will essentially be one-click navigation 

Global Training Manager
SCADA & Telemetry
Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-01-03 01:56 AM
0 Likes
3
1510
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-03 01:56 AM

Re: Geo Map object left mouse click

Hi @Jimi 

Unless GeoSCADA Expert has changed in the past few weeks, the Map displays are not standard Mimics. They don't really have layers that can be freely configured with mimic objects etc.

It's just an embedded webkit engine which has a javascript WMS engine streamed into it, and some hooks into the ClearSCADA query engine.

 

There are ways to get data into the map displays, via customised User Queries which can return HTML that the webkit engine can then follow.  But to do such it would first need to pull up the POI popup, which would require browsing over a POI.. then it would need a click within the POI popup.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Share
Reply
Johnny07
Crewman Johnny07
Crewman
‎2020-01-03 02:22 AM
0 Likes
2
1502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-03 02:22 AM

Re: Geo Map object left mouse click

Jimi, thanks for your reply.

 

but like bevan_weiss said i think this is not possible because this i not a standard mimic, but it is generated.

i could be that i don't understand what you mean, but if it is still possible could you give me some more details.

 

Thanks for your answer anyway.

Share
Reply
Johnny07
Crewman Johnny07
Crewman
‎2020-01-03 02:31 AM
0 Likes
2
1501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-03 02:31 AM

Re: Geo Map object left mouse clickT

Thanks for your answer, it might be a solution for us. we will try solving it this way.

 

what is see now is we have popup on the POI, it is visible when i hover over it.

but the popup disappears when i move the mouse to the popup because the mouse is leaving the POI, example below.

any advise?

 

Thanks for your answer.

 

poi.JPG

 

 

 

 

Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-01-03 02:43 AM
0 Likes
1
1493
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-03 02:43 AM

Re: Geo Map object left mouse clickT

Ohh yes, I remember this behaviour now.

I don't think I ended up looking into it any more beyond that sorry.

 

I'd probably try a slightly larger popup, add some more content, maybe just another 4 or 5 blank lines.

I have a recollection of being able to have the cursor over the popup, and to highlight text etc.  But this might just be my bad memory telling me lies.

 

It's probably something that is worth contacting your local Tech Support about, if for nothing else than so that they can put your comments against an enhancement request.  So that your use case is captured.

Schneider are generally quite responsive on such things if there is enough interest, and it's always good to have your comments with the vendor anyway... it means they don't just walk their own way down the windy road...


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
Johnny07
Crewman Johnny07
Crewman
‎2020-01-04 03:34 AM
0 Likes
0
1481
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-04 03:34 AM

Re: Geo Map object left mouse clickT

Thanks for this additional info, i will test the option with blank lines.

and contact support.

 

Thanks again,

 

Johnny

 

Other advices still welcome!

Share
Reply
Jimi
Lt. Commander Jimi Lt. Commander
Lt. Commander
‎2020-01-06 01:10 AM
0 Likes
1
1461
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-06 01:10 AM

Re: Geo Map object left mouse click

Hi Johnny,

I just tested what @BevanWeiss said & it's correct. I wasn't clear to me you were using map objects, what I suggested will only work on regular mimics. 

Global Training Manager
SCADA & Telemetry
Share
Reply
Johnny07
Crewman Johnny07
Crewman
‎2020-01-06 05:02 AM
0 Likes
0
1455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-01-06 05:02 AM

Re: Geo Map object left mouse click

Jimi, Thanks for your additional testing and posting your results.

 

We do some tests with the POI popup, else we need to use the right click menu.

 

Thanks,

 

Johnny

Share
Reply
Top Experts
User Count
sbeadle
Sisko sbeadle Sisko
1
geoffpatton
Lieutenant geoffpatton
1
BevanWeiss
Admiral BevanWeiss
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric