Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • SCADA & Telemetry Solutions
  • :
  • Geo SCADA Expert Forum
  • :
  • Export ClearSCADA Historic Data
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49223members
Join Now
242430posts
Join Now

Export ClearSCADA Historic Data

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Geo SCADA Expert Forum
Solved
DavidSkilbeck
Lieutenant DavidSkilbeck
Lieutenant
‎2020-06-30 04:54 PM
0 Likes
6
990
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-30 04:54 PM

Export ClearSCADA Historic Data

Hi, I refer to https://www.se.com/ww/en/faqs/FA312272/.

 

Where it mentions WKxxxxxx.hrd files.

Can these .hrd files be copied from one GeoSCADA machine and pasted in to the appropriate folder of another. GeoSCADA machine?

 

(Example of folder path - C:\ProgramData\Schneider Electric\ClearSCADA\Database\History\Historic\HdI02382\609845)

Would the GeoSCADA machine with pasted files, then pick up on these files or would we have to import / configuration?

 

The ultimate goal of this post is to investigate if .hrd file can be copied over from one GeoSCADA machine and used in another.

 

Thanks,

 

Solved! Go to Solution.

Labels
  • SCADA
Tags (1)
  • Tags:
  • english
Share
Reply

Accepted Solutions
JChamberlain
Lieutenant JChamberlain Lieutenant
Lieutenant
‎2020-07-02 06:33 PM
0 Likes
3
956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-02 06:33 PM

Re: Export ClearSCADA Historic Data

Sure, you can do it and it will work most of the time, but by doing this method you bypass database locking. Don't raise a case with support when the data is incomplete or corrupted, or the server raises alarms about not being able read historic data!

 

There are methods built in to do this, use them.

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
6 Replies 6
JChamberlain
Lieutenant JChamberlain Lieutenant
Lieutenant
‎2020-06-30 06:57 PM
0 Likes
5
983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-30 06:57 PM

Re: Export ClearSCADA Historic Data

In your example, 609845 is the object ID for the point that generated the historic data. Whichever object ID is there on the destination system is the object that the data will be added to. There will need to be an existing point configured with that object ID.

 

When copying and pasting database files, the system should be stopped to avoid issues with flushing and file access, but as Steve said in the other topic it's not an ideal way to do it.

 

Have a read of this page on streams.

Tags (1)
  • Tags:
  • english
Share
Reply
DavidSkilbeck
Lieutenant DavidSkilbeck
Lieutenant
‎2020-07-02 03:57 PM
0 Likes
4
958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-02 03:57 PM

Re: Export ClearSCADA Historic Data

Hi, I created a point in one GeoSCADA vm and created a .hrd file for that point.
Then copied the .hrd file over to another GeoSCADA vm where I had created another point of the same name.
Restarted that GeoSCADA and it picked up on the copied file.

In practise stopping the first GeoSCADA machine in order to copy the file would be an issue.

Not so for the second GeoSCADA machine.
Thanks,

 

 

Tags (1)
  • Tags:
  • english
Share
Reply
JChamberlain
Lieutenant JChamberlain Lieutenant
Lieutenant
‎2020-07-02 06:33 PM
0 Likes
3
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-02 06:33 PM

Re: Export ClearSCADA Historic Data

Sure, you can do it and it will work most of the time, but by doing this method you bypass database locking. Don't raise a case with support when the data is incomplete or corrupted, or the server raises alarms about not being able read historic data!

 

There are methods built in to do this, use them.

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
DavidSkilbeck
Lieutenant DavidSkilbeck
Lieutenant
‎2020-07-06 07:35 PM
0 Likes
2
928
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 07:35 PM

Re: Export ClearSCADA Historic Data

Hi, can you please elaborate on "There are methods built in to do this, use them.".
Which methods do you refer to exactly.

Thanks,

Tags (1)
  • Tags:
  • english
Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-07-06 10:43 PM
0 Likes
1
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 10:43 PM

Re: Export ClearSCADA Historic Data

I reckon Jesse will be talking about these

https://tprojects.schneider-electric.com/telemetry/display/public/CS/Adding+Historic+Data+to+Points


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (1)
  • Tags:
  • english
Share
Reply
DavidSkilbeck
Lieutenant DavidSkilbeck
Lieutenant
‎2020-07-06 10:55 PM
0 Likes
0
918
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 10:55 PM

Re: Export ClearSCADA Historic Data

Oh, yes. I have used this before.
Thanks,

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
BevanWeiss
Admiral BevanWeiss
2
sbeadle
Sisko sbeadle Sisko
1
geoffpatton
Lieutenant geoffpatton
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric