Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • SCADA & Telemetry Solutions
  • :
  • Geo SCADA Expert Forum
  • :
  • Execute structured text program with pick param and pick type animation
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51132members
Join Now
245263posts
Join Now

Execute structured text program with pick param and pick type animation

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Geo SCADA Expert Forum
Solved
Tanquen
Lt. Commander Tanquen
Lt. Commander
‎2020-10-05 06:29 PM
0 Likes
2
372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-05 06:29 PM

Execute structured text program with pick param and pick type animation

The current application has two checkboxes, one to disable the tags alarm with the '?Digital.Disable' and one to set a PLC bit for that alarm with the '?Control&Value="1"'. They have some level alarms that were four separate alarms that they now want combined so that was easy enough to add a calculation digital point and disable the four alarms. Now just the calculation digital point goes into alarm when any of the four are true and the checkbox just disables the new calculation digital point.

 

Now I'm trying to figure out how to make the one check box toggle the four PLC bits. Working with buttons I know you can't just have a pick action method set four values at once so I made a structured text program to look at one of the bits and if it's true make them all faults if it's false make them all true. 

 

It's easy enough to make the pick action method with the structured text object selected and then the method set to execute and it works but for the life of me I can't figure out how to get it to work with the pick param and pick type animation. I know there's an execute method in the schema so I must have the syntax or the spelling or something wrong but it never does anything and it's really frustrating because the pick action keeps getting setup and it's confusing as to which ones actually working. The pick param and the pick type that you've configured under animations or the pick action that also looks like it's set up. I'm using pick type 5 and I think that should work with the execute method. I did try the others 17 and 19 and 20 and whatever and none of those work and they only seem to work with VB. Also the example for 19 makes it look like you can just put a message box command with a string and have it work and their example doesn't work.

 

So this works in a pick animation:

SCX:////CLogicSTProgram/...Tags DNP.Bioxide.Calcium Nitrate Tank 6701.Level SP.Toggle Rdy Tags

Untitled.jpg

 

 

But this don't work in a pick param animation:

 

"SCX:////CLogicSTProgram/...Tags DNP.Bioxide.Calcium Nitrate Tank 6701.Level SP.Toggle Rdy Tags"+'?Execute'

Solved! Go to Solution.

Labels
  • Logic
  • Scripting
  • ViewX
Tags (13)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA control
  • SCADA data
  • SCADA integration
  • SCADA network
  • SCADA programming
  • SCADA software
  • scada system
  • SCADA tutorial
  • SCADA web application
  • Telemetry and SCADA
Share
Reply

Accepted Solutions
Hardin4019
Lieutenant Hardin4019
Lieutenant
‎2020-10-07 06:00 AM
1 Like
1
349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-07 06:00 AM

Re: Execute structured text program with pick param and pick type animation

Drop the SCX:////CLogicSTProgram/ and try again. I did a test with PickType 5 and PickParam ".PickActionTest.ObjectLink"+'?Execute' that executes a ST that toggles an internal point form 0 to 1 and back. Worked like a champ. 

See Answer In Context

Tags (13)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA control
  • SCADA data
  • SCADA integration
  • SCADA network
  • SCADA programming
  • SCADA software
  • scada system
  • SCADA tutorial
  • SCADA web application
  • Telemetry and SCADA
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
2 Replies 2
Hardin4019
Lieutenant Hardin4019
Lieutenant
‎2020-10-07 06:00 AM
1 Like
1
350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-07 06:00 AM

Re: Execute structured text program with pick param and pick type animation

Drop the SCX:////CLogicSTProgram/ and try again. I did a test with PickType 5 and PickParam ".PickActionTest.ObjectLink"+'?Execute' that executes a ST that toggles an internal point form 0 to 1 and back. Worked like a champ. 

See Answer In Context

Tags (13)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA control
  • SCADA data
  • SCADA integration
  • SCADA network
  • SCADA programming
  • SCADA software
  • scada system
  • SCADA tutorial
  • SCADA web application
  • Telemetry and SCADA
Share
Reply
Tanquen
Lt. Commander Tanquen
Lt. Commander
‎2020-10-07 08:26 AM
0 Likes
0
339
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-07 08:26 AM

Re: Execute structured text program with pick param and pick type animation

Thanks, I'm so confused as to the best way to go. Since I couldn't get that to work I ended up putting the check box inside the group with the rest of the tags and the structured text object. Now I just have to drag the checkbox onto the screen and it's already linked. I was trying to figure out a way to use parameters to have the checkbox on the screen and then drag the structure text object onto it. I think it's better having it already linked but now it's completely different than all the other check boxes. They sure don't make the syntax on any of the number of ways you can do stuff easy. I put the SCX prefix on there because it's on there in the pick action wizard so you would think it would be similar using the pick param. I was also missing the .objectlink.

Tags (13)
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA control
  • SCADA data
  • SCADA integration
  • SCADA network
  • SCADA programming
  • SCADA software
  • scada system
  • SCADA tutorial
  • SCADA web application
  • Telemetry and SCADA
Share
Reply
Top Experts
User Count
sbeadle
Sisko sbeadle Sisko
188
BevanWeiss
Sisko BevanWeiss
52
AdamWoodland
Lt. Commander AdamWoodland Lt. Commander
16
JChamberlain
Lieutenant JChamberlain Lieutenant
16
AndrewScott
Lieutenant AndrewScott
15
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric