  • Create a new Object using ST
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51132members
Join Now
245263posts
Join Now

Create a new Object using ST

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Geo SCADA Expert Forum
Solved
BevanWeiss
Sisko BevanWeiss
Sisko
‎2020-06-14 12:31 AM
0 Likes
5
571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-14 12:31 AM

Create a new Object using ST

Hi all,

I really thought I'd done this before, but I can't find any example of it in my at-hand databases.

 

I'm looking to automatically create Operator Document Stores for User accounts that don't already have them.

 

I know that this could be done using a couple of SQL queries to INSERT a new row into the Operator Document Store table, and to then UPDATE the CDBUserViewXConfig table with the new OperatorDocStoreId.

But I'm not a huge fan of the SQL form here.  I'd much rather something like CGroup.CreateNew("Operator Document Store", "freddie");

 

Am I just delusional that this would be possible using a Method or similar from ST?


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

Solved! Go to Solution.

Labels
  • SCADA
Share
Reply

Accepted Solutions
sbeadle
Sisko sbeadle Sisko
Sisko
‎2020-06-15 12:47 AM
0 Likes
4
561
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-15 12:47 AM

Re: Create a new Object using ST

Hi Bevan,

there's no exposure of the COM or .Net Client style methods to create objects in Logic. If it were that easy I can't imagine the follow-on problems it might cause! 😀

Steve

See Answer In Context

Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
5 Replies 5
sbeadle
Sisko sbeadle Sisko
Sisko
‎2020-06-15 12:47 AM
0 Likes
4
562
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-15 12:47 AM

Re: Create a new Object using ST

Hi Bevan,

there's no exposure of the COM or .Net Client style methods to create objects in Logic. If it were that easy I can't imagine the follow-on problems it might cause! 😀

Steve

See Answer In Context

Share
Reply
AdamWoodland
Lt. Commander AdamWoodland Lt. Commander
Lt. Commander
‎2020-06-16 08:09 PM
0 Likes
0
542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-16 08:09 PM

Re: Create a new Object using ST

Could use SYSTEM() to call some app or script on disk is another option

Tags (1)
  • Tags:
  • english
Share
Reply
BevanWeiss
Sisko BevanWeiss
Sisko
‎2020-06-17 05:07 AM
0 Likes
2
534
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-17 05:07 AM

Re: Create a new Object using ST

Lol... I'm creating objects via SQL from ST... is that better @sbeadle ? 😛

I think it would have been 'cleaner' if I could have called like a 'Create( 'TypeDesc', 'Name' )' method on the parent group from ST, and just passed in those items.

Even better of course if it would return the ID of the newly created object... then I could easily update the OperatorDocStoreId 🙂

 

That is some bold out of the box thinking from @AdamWoodland on the SYSTEM() command idea though 😮

I very much dislike it however, and I think I do prefer my SQL ST calamity.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (1)
  • Tags:
  • english
Share
Reply
AdamWoodland
Lt. Commander AdamWoodland Lt. Commander
Lt. Commander
‎2020-06-17 04:20 PM
0 Likes
1
518
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-17 04:20 PM

Re: Create a new Object using ST

Logic is too disjoint from the database for that, property writes and %D SQL execution happens long after the logic has finished executing. During the execution they are just put onto a stack.

 

The logic process is documented at https://tprojects.schneider-electric.com/telemetry/display/CS/Logic+Execution

 

I figured you might not like the SYSTEM() option, I wasn't too keen on that idea myself but how good it might work is very customer specific 🙂

Tags (1)
  • Tags:
  • english
Share
Reply
BevanWeiss
Sisko BevanWeiss
Sisko
‎2020-06-18 04:37 AM
0 Likes
0
512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-18 04:37 AM

Re: Create a new Object using ST

Hi @AdamWoodland,

 

I was thinking something like the Expression engine Method Tags, where a Method can be called which returns a result.

You're right, that it wouldn't really work with the INPUT>PROCESS>OUTPUT structure of the Logic engine however.

 

I could probably do it using a second ST Logic routine, and indirect addressing... but then I'm tying together an SQL INSERT (called by ST logic) and the calling of a second ST Logic routine... I'm not sure entirely how the timing around these would be performed.. so I think it's probably less risky to stay in either SQL or direct ST output manipulation and not do a little of both..

 

You did make me read about the NOCACHE stuff again, and I forgot that they can apply for normal Input data as they can for SQL inputs.  I'm sure I can find some more places tomorrow to go sprinkly through NOCACHE references...

 

 

My next problem around the Operator Document Stores is regarding the security permissions, and the need for CFG... (and I guess more annoyingly having to break the security inheritance).  It would be nice if security could be implemented as a 'delta' type of operation without breaking inheritance... i.e. I want everything just like the ParentGroup.. except ADD CFG for this person.  or SUB CFG for this group (if it did have CFG from the parent).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
sbeadle
Sisko sbeadle Sisko
188
BevanWeiss
Sisko BevanWeiss
52
AdamWoodland
Lt. Commander AdamWoodland Lt. Commander
16
JChamberlain
Lieutenant JChamberlain Lieutenant
16
AndrewScott
Lieutenant AndrewScott
15
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric