  • ClearSCADA 2017 - Move the value of one of two different tags based on discrete into a third tag
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49232members
Join Now
242447posts
Join Now

ClearSCADA 2017 - Move the value of one of two different tags based on discrete into a third tag

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to Geo SCADA Expert Forum
Tanquen
Lt. Commander Tanquen
Lt. Commander
‎2020-04-13 06:44 PM
0 Likes
6
846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-04-13 06:44 PM

ClearSCADA 2017 - Move the value of one of two different tags based on discrete into a third tag

So if the discrete tag is true display tag A is used, if false then display the value from tag B.

I know I could just use visibility with two objects on the screen but would like a third tag that would show the value, historical data and alarms from one or the other at all times.

Labels
  • SCADA
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
6 Replies 6
JChamberlain
Lieutenant JChamberlain Lieutenant
Lieutenant
‎2020-04-14 01:45 AM
0 Likes
5
836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-04-14 01:45 AM

Re: ClearSCADA 2017 - Move the value of one of two different tags based on discrete into a third tag

Do you want to do this for existing history, or are you ok with just getting data from when you implement it?

 

Sounds like a job for a calculation point, but it won't backfill anything. For that you'd need to write some logic or something in one of the APIs.

Share
Reply
Tanquen
Lt. Commander Tanquen
Lt. Commander
‎2020-04-14 08:45 AM
0 Likes
4
827
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-04-14 08:45 AM

Re: ClearSCADA 2017 - Move the value of one of two different tags based on discrete into a third tag

That sounds complicated. 🙂 The PLC work is being done by others but it seems like you should be doing this in the PLC so the SCADA just has one tag.

 

My current understanding is that you would have an analog internal tag with level alarms and historical logging that would somehow be getting its value from one of two external analog I/O tags. They currently have two discrete tags to choose between two different analog tags or addresses. If discrete A is set then switch the analog internal tag to get its value from external analog tag A and then the same for another set of B tags. So the one analog internal tag displayed on the screen would have the alarms and historical data of the sensor in charge of the process.

 

I’ve not worked with ClearSCADA very often and wanted to see what the options were. Was there something like “calculation point” that you mentioned that would remap the data to a new internal tag or a way to change an external analog tags I/O address reliably on the fly?

 

Thanks for taking a look.

Share
Reply
JChamberlain
Lieutenant JChamberlain Lieutenant
Lieutenant
‎2020-04-14 07:47 PM
0 Likes
3
816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-04-14 07:47 PM

Re: ClearSCADA 2017 - Move the value of one of two different tags based on discrete into a third tag

Yep, a calculation point is an internal database point that has an expression so you could have something like (psuedocode):

 

If (discrete)

then (analogX)

else (analogY)

 

You can configure it to be triggered by various means and it will add the data each time.

 

You can configure changing of the IO address on the fly, but I wouldn't recommend it. Dynamic config should be avoided for performance reasons - it has to be re-validated, re-added to the driver etc.

Share
Reply
sbeadle
Sisko sbeadle Sisko
Sisko
‎2020-04-15 12:15 AM
1 Like
2
810
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-04-15 12:15 AM

Re: ClearSCADA 2017 - Move the value of one of two different tags based on discrete into a third tag

The syntax for the expression is:

IIF( ".test point.CurrentValue"=1,".pointWhenOne.CurrentValue",".pointWhenZero.CurrentValue")

Share
Reply
JChamberlain
Lieutenant JChamberlain Lieutenant
Lieutenant
‎2020-04-15 12:18 AM
0 Likes
1
807
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-04-15 12:18 AM

Re: ClearSCADA 2017 - Move the value of one of two different tags based on discrete into a third tag

Thanks for covering for my laziness Steve!

Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-04-26 04:20 AM
0 Likes
0
749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-04-26 04:20 AM

Re: ClearSCADA 2017 - Move the value of one of two different tags based on discrete into a third tag

I find laziness works sometimes.. I prefer allowing the default property to take over, this way the 'point' doesn't even need to be a point, it could also be a Variable, or a Parameter (and I haven't yet seen ClearSCADA get the default property wrong... although you'll get the bug report the instant I do Jesse 😛 )

 

IIF( ".test point", ".pointWhenTrue", ".pointWhenFalse" )


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
Related Products
Schneider Electric
EcoStruxure™ Geo SCADA Expert
Top Experts
User Count
BevanWeiss
Admiral BevanWeiss
2
sbeadle
Sisko sbeadle Sisko
1
geoffpatton
Lieutenant geoffpatton
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric